EV charger causing ground overheating | Page 3 | on ElectriciansForums
Discuss EV charger causing ground overheating in the UK Electrical Forum area at ElectriciansForums.net
redfox88
Ireland
Had an EV charger installed in July last year. It’s wired directly off the mains.
Since end of November anytime I plug the car in to charge, the earth/ground wire in the cabling in other appliances in the house is overheating and melting components of the appliance until the main RCD trips.
Has anyone ever seen or heard this happening before and what could be happening?
Even appliances isolated by switch fuses, when off are getting impacted. It’s concerning.
Electrician has been doing tests but is not quite sure what could be causing the fault
That appliance should have been earth bonded but it wasn’t. Perhaps why it was the victim or some other strange reason.
It's a likely contender if it is connected to metallic water or gas mains that were providing the best earth path after the CNE broke open. As you say, adequate main bonding would then have prevented damage to the wiring by diverting the current along a much heavier conductor. But... would you have discovered the problem in that case, or would the pipework have been left carrying the entire house load current for the foreseeable future?
Some of us here are not huge fans of TN-C-S, even in its PME guise.
We also found that when we had the combi boiler installed early last year and new pipework done to meet spec, that the gas engineer never did any earth bonding on those pipes, nor did they say anything about needing to do it.
We also don't believe gas is earth bonded at the mains, despite certs from electricians, including more recently the EV install cert, claiming it is.
Strangely enough, networks called again today to upgrade the meter they installed yesterday to a new smart meter.
Recommendation again is to attach more sufficient earth cable from us to them, but also replace the black and red mains cables, the luxury for which will cost €160 for them to call out while that work is being carried out...I think that's what I read from the conversation any way. But he said the red and black were large enough for this not to be done immediately, although its near top of the list now with everything that's happened recently
Under the current regs, when all relevant circuits are RCD protected, the requirements and necessity of supplementary bonding e.g. around the boiler are largely eliminated. But where there are extraneous metallic service pipes, which it seems you might have, main bonding is mandatory and all the more so with TN-C-S supplies.
Not withstanding what was a dangerous installation regardless of the EV charger, am left wondering why the EV charger did not detect an open PEN and shut down or at least there should have been a rod for the EV charger.......... think the OP would do well to get an electrician to go through the install with a fine tooth comb
From the charger's point of view, it wasn't open-circuit. There was still continuity, just via the wrong conductors. There would have been extra voltage drop on account of their smaller CSA but perhaps not enough to signal an abnormal condition
Suppose it depends how it has been implemented in the EV charger. With what the OP was saying about hot earth cables around the property, i would expect to see unusual voltages and currents as measured at the EV charger, The Zappi for example has that many reference points built in to the charger that it has occasion shut down when there was no PEN issue, lol - Still think its one to note
New fuse and meter supplied and readings they’re getting all good.
Their only comment was on the earth cable going from our unit into theirs, that it was too small but not major. Something to fix whenever electrician is out again
The EV chargepoint shouldn't have been installed if the main protective conductor (neutralising link) was undersized. This should have been rectified first.
PEN fault disconnection is not a requirement of I.S. 10101.
There are differences between Irish and UK regs and as far as I know an earth electrode is required for the whole installation under Irish regulations when a TNCS supply is used.
Just had a browse on some chargers and the Tesla for example would have seen the rod and concluded no problem, assuming Earth fault detection was enabled for that install. I am pretty sure a Zappi would have gone nuts either with under-voltage L-N or N-E v Diff
Interesting though how to melt your house cables,
UPDATE: came home from a couple nights away to no power in the house. The main RCD had tripped.
I traced issue to blow 3A fuse in the switched fuse spur powering the gas boiler. I replaced the 3A fuse but the boiler didn't power.
Further inspection inside the boiler should me that the small fuse inside the boiler had blown.
And further inspection again showed me cabled inside the boiler had been overheating. The loom connecting all the components was melting, and the cables connecting those components to the pub had been melting too. Absolutely no idea why. Power to boiler is sound and no issues anywhere else on the circuit except for the boiler.
Gas boiler installer and repair guy is calling to replace entire boiler as opposed to just components and wiring from the last time round.
It sounds like a possible fault with the supply N
this may be somewhere along the supply cable or even at the substation.
a call to your energy supplier emergency hotline is the best place to start.
Reply to EV charger causing ground overheating in the UK Electrical Forum area at ElectriciansForums.net
This is a baffling fault I've been fighting with for a couple of weeks now, so I wondered if another set of eyes will help. I installed an EV...
He only posted the one message then never came back.