This is a baffling fault I've been fighting with for a couple of weeks now, so I wondered if another set of eyes will help.

I installed an EV Charger a few weeks back, and all went well for a while, then the client called me to say it wasn't charging randomly. Resetting it brought it back to life. When we interrogated the logs we were seeing a combination of Earth Fault and PEN Fault errors.

I retested everything right through and found no issues with regarding earthing, continuity and IR. I even did a full EICR on the house, with no issues found. (It needed it anyway, as the client had requested a new consumer unit).

Both the manufacturer and the DNO have been contacted and they acknowledge the fault but they are also at a loss as to what it is.

The only thing I noticed is the incoming voltage. Normally I see a reasonably stable voltage at a property, but in this case it was wobbling all over the place from 230V up to 247V. Unfortunately the DNO will not send out an engineer unless the voltage falls outside the range of 213V to 253V. But I was thinking, if the voltage is unstable and it suddenly dropped below 213V could it cause the EV Charger to throw a wobbly and misreport an Earth Fault ?

The only other thing, is to check for current leakage on the earth, but I can't remember how I can monitor that.

Oh finally the RCBO's are not tripping when this happens.

Any thoughts welcome.
 

Reply to EV Charger reporting PEN Fault in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
295
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
277
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

  • Question
Except where provided by the EV charging equipment, protection against DC fault currents shall be provided by: (i) an RCD Type B, or (ii) an RCD...
Replies
5
Views
824
They won't do groundworks but you can get a quote from them for an EV charger install. https://octopus.energy/get-an-ev-charger/
Replies
37
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top