you were winding me up willder about 20 degrees on zs... bet you scitter when younger,,,,

Oi I'm still young (ish)

Zs reference was valid, but shouldn't be a concern for you with a 2382-10 exam. It's more of a 2391 question. I can explain further if you like, if you have the OSG it will be simple to explain.
 
BS 7671 does.
Yes BS7671 states that the designer should recommend the interval for when the first PIR should take place.
Then GN3 states, that the inspector carrying out the initial verification should recommend when the first PIR will be required.
Nice to see such co-ordination between the publications.
 
Last edited by a moderator:
Yes BS7671 states that the designer should recommend the interval for when the first PIR should take place.
Then GN3 states, that the inspector carrying out the initial verification should recommend when the first PIR will be required.
Nice to see such co-ordination between the publications.

I think it would be wiser to advise the right information in this thread though, don't you?
 
1) BS7617 is a non-statutory document, but if it is adhered to, compliance with which statutory document is likely to be achieved?
2) When may non-rechargeable auxiliary batteries be used in caravans?
3) With a DC voltage of 125V between conductors how would the installation be classified?
4) What is the most likely cause of an overload current arising in an electric motor circuit?
5) Under what conditions is the design current of a circuit defined?
6) Name a type of lighting equipment likely to require additional protection against thermal effects?
7) A component of a support system consisting of regularly spaced elements which mechanically retain a cable is defined as?
8) Name 3 SELV sources that will provide combined basic and fault protection?
9) A protective device giving protection to both overload and short circuit must be capable of breaking current up to what level?
10) A 230V single-phase heating circuit has a design current of 25A. The length of the PVC insulated cable is 20m. The 4mm[SUP]2[/SUP] cable installed has a volt-drop of 11mV/A/m. The voltage drop under full load conditions is? And does this comply with BS7671?
 
Last edited by a moderator:

Reply to the thread, titled "everynights a 17th edition night" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top