ask me questions, see if i can find in appropiate time, no trick ones please only if you have nothing better to do..
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss everynights a 17th edition night in the Australia area at ElectriciansForums.net
i thought multiply by 1.6 , as 20 degrees isnt in red book i guestimated 1.6 using the sequence..... so does this be done in the real world???? ive seen in some thread that you multiply by 1.2 is that figure normal used for safe side???
so much to consoder i bettter get 20 an hour when im finished this course lol
i thought 30 degrees = 1 but am i on about current carring capacity
at high tide or low tide, that is the question.At a marina on a floating walkway or pontoon what height can you install a socket outlet?
11x25x20/1000= 5.5v so complies but do i need todo anything for full load markie sparkie ... or anyone if you out there cheers markie sparkie you can mark now1) BS7617 is a non-statutory document, but if it is adhered to, compliance with which statutory document is likely to be achieved?
2) When may non-rechargeable auxiliary batteries be used in caravans?
3) With a DC voltage of 125V between conductors how would the installation be classified?
4) What is the most likely cause of an overload current arising in an electric motor circuit?
5) Under what conditions is the design current of a circuit defined?
6) Name a type of lighting equipment likely to require additional protection against thermal effects?
7) A component of a support system consisting of regularly spaced elements which mechanically retain a cable is defined as?
8) Name 3 SELV sources that will provide combined basic and fault protection?
9) A protective device giving protection to both overload and short circuit must be capable of breaking current up to what level?
10) A 230V single-phase heating circuit has a design current of 25A. The length of the PVC insulated cable is 20m. The 4mm[SUP]2[/SUP] cable installed has a volt-drop of 11mV/A/m. The voltage drop under full load conditions is? And does this comply with BS7671?
at high tide or low tide, that is the question.
I'm a little confused here;I've read this thread which was started by i=p/u , who i wholeheartedly respect on this forum, however what i can not fathom is this; are you doing a course on what i understand to be BS 7671 ? or are you doing the C&G 2391 ?
The reason i ask is, if you are doing 17th edition BS 7671, then this exam is open book, multiple question {(which means, an exam to show that you can read a book and find relevant answers to questions quickly in said book),The BRB soon to be The BGB}, where you should PASS with no less than 99% in your case. If however i read it at wrong, and you do indeed are doing the 2391, then pm me, as i have loads of help at your disposal.
Marnik
Minimum CSAs for flexes and cables for caravan connections I=P/U.......table and page no. please.......