Many thanks to 'Dave_' for posting this example originally in a thread.


Minimum Size of CPC

Here I will calculate the minimum size of CPC in accordance with regulation 541.1.3 of BS7671.
Primarily I will need to calculate the minimum size of CPC (or confirm the armouring is adequate) of the distribution cables. I already know that the external loop impedance value is 0.08Ω, so I will now focus on the distribution cable to the distribution board, and secondly the supply cable between the suppliers cut-out and the CCU.
I have used data from AEI cables (this can be found in the index) to ascertain the values for conductor and armour resistance.
Distribution circuit to DB3
I will use the equation: Zs = Ze(R1+R2)
Ze = 0.08
R1 = 0.342 mΩ/m (at 90°C, i will not need to apply a correction factor of 1.28)
R2 = 1.2 mΩ/m (armour resistance)
Circuit length = 24m
Therefore: 0.342 + 1.2 = 1.542 mΩ/m × 24 = 37mΩ or 0.037Ω
0.037 + 0.08 = 0.117Ω
I can now calculate the fault current using the following equation:

If= Uo/Zs
Where If = fault current, Uo = line voltage to earth and Zs = total loop impedance
If= 230/0.117=1966A
Using Amtech software at work I have sourced the relevant time current graphs for SQUARE-D BSEN 60947-3 MCCB’s which I will use in the installation (I will go into more detail in part 7, time current graphs can be found in the index)
Using time current graph number 1: t = 0.1s @ 1966A
This is perfectly acceptable, maximum disconnection time = 5 seconds (over 32A)

I will now use the adiabatic equation below to confirm that the armouring of the cable can withstand the level of fault current:
S= √(I²×t)/k

Values for k can be found on p129 BS7671 (in this case table 54.4, the armour of a cable)

S= √(1966²×0.1)/46=13.5mm²

Using the table provided by AEI I can see that a 70mm² four core cable has a 131mm² armour CSA, therefore this is perfectly acceptable.
 
Last edited by a moderator:
Found that the other day, really usefull for me and cleared up 99% of any confusion I had.

Registered with AEI cables website, loads of info on data sheets, very handy
 
Even better still would be if he got the formula right

Zs = Ze + (R1+R2)

not the one shown which means Zs = Ze x (R1+R2)
 
Last edited:
Im a bit confused when trying this out to work out an earthing conductor?
I take it that the fault current would be the PFC so if say trying to work it out for a TNS system

230/0.8= 287.5a, seems a bit low, what am I doing wrong?
 
its right. bear in mind the higher the resistance, the lower the current that wuill flow. 0.8 is the abolsute max Ze that you will have if you are supplied with an earth from the REC. so 287a should be the least amount of fault current you will have also, (assuming 230v).

i remeber when i was doing 2360, that they were telling us about the debate for PME, and one of the issues was that the lower Ze, wopuld cause higher fault currents, and increase the risk of fire, in poorly maintained installations.

The flip side is that along with increased fault currents come quicker disconnection times, which is i believe the driving force behind PME.
 
Thanks Johnboy6083, I just couldn't believe how low that was, cheers for the reassurance.
 
I will now use the adiabatic equation below to confirm that the armouring of the cable can withstand the level of fault current:
S= √(I²×t)/k


Adriatic :)
[video=youtube;wHidlxvO0pg]http://www.youtube.com/watch?v=wHidlxvO0pg[/video]
 
I note you use the resistance value of R2 = 1.2 mOhms per metre for the armour, does the armour have no reactance? or if so is it so small as to be ignored in calculating earth fault loop impedance values. Ignoring the reactive component would give a lower earth fault loop impedance and hence a higher earth fault current than would occur if reactance was taken into account.
 
I note you use the resistance value of R2 = 1.2 mOhms per metre for the armour, does the armour have no reactance? or if so is it so small as to be ignored in calculating earth fault loop impedance values. Ignoring the reactive component would give a lower earth fault loop impedance and hence a higher earth fault current than would occur if reactance was taken into account.

You should take reactance into account in the armour
 
Chr!s, It is also my view that armour reactance should be taken into account. The example posted by Lenny only mentions resistance.
Do you know the reactance values for the armour of all BS standard armoured cables for both copper and aluminium conductors, 2 core, 3 core and 4 core?
I have searched the internet unsuccessfuly many times.

Regards

Wilbur
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Example of use of Adiabatic Equation.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
48

Advert

Thread statistics

Created
Guest123,
Last reply from
James-,
Replies
48
Views
81,293

Advert

Back
Top