There is a more complete (and technically accurate) definition just above table 43.1.Resistivity of the material the conductor is made of, taking into account temperature and heat capacity of the conductor material.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Example of use of Adiabatic Equation. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
There is a more complete (and technically accurate) definition just above table 43.1.Resistivity of the material the conductor is made of, taking into account temperature and heat capacity of the conductor material.
so im trying to work out the minimum size main earth for main supply ze=0.11 its a tncs supply i would say k=143 and for the main consumerunit i would say its 5 second disconection time so
230/0.11=2091
so doing the caculation i get 32.9mm and this cant be right what am i doing wrong it must be T
a bs 1361 will go quicker than 0.1 s at that fault curent.
so taking pg 244 time/current characteristics for 1361 60 a fuse at 5 seconds is 330A so doing the calc again i get 5.16mm this is better but what is right or for a consumerunit disconection time is it 0.4
please help i done it on a pir with a 6mm main earth which i doubled up to 12mm but minimum size is 5.16mm now this is safe just not conforming to bs7671 2008