marcuswareham
Arms
Instead of making a metal outbuilding TT and having a high impedance electrode and then relying on RCDs and having the possibility of 2 earthing systems in close proximity, could you use an earth electrode (for measurement only) and a voltage monitoring relay that opens a contactor (L, N & PE) if the voltage between PME earth and the electrode is >50v , although I guess there is a risk of N current and fault current going down said electrode if things went wrong so would probably need 10mm bonding, doh ?
Can 722.411.41 (iv) be applied to a metal outbuilding using a PME earth also, so using a voltage sensing relay and a contactor to break L, N & PE if the voltage is outside of 207v - 253v, to lower the risks (although doesn't make them go away), I know 722.411.41 is for EV but but could the same idea be used in this case
Can 722.411.41 (iv) be applied to a metal outbuilding using a PME earth also, so using a voltage sensing relay and a contactor to break L, N & PE if the voltage is outside of 207v - 253v, to lower the risks (although doesn't make them go away), I know 722.411.41 is for EV but but could the same idea be used in this case