Extending ring main with wago 222 | on ElectriciansForums

Discuss Extending ring main with wago 222 in the UK Electrical Forum area at ElectriciansForums.net

Joined
Oct 24, 2022
Messages
13
Reaction score
1
Location
United Kingdom
I have come to extend a ring main on the old wiring (red and black) and have used the wago 222 connectors to extend each leg and extended each leg in a wago junction box and are all connected in the ceiling screwed to joists. The wago 222’s are rated at 32A but when used maintenance free like I have they’re de rated to 20A. The ring is on 32A RCBO, will it be safe with each leg extended with the 222’s even as they’re derated to 20A because they’re in a MF box in the ceiling? Thanks
 
Welcome to the forum mate.
You will be ok with using 222 for extending ring circuits.
If you are concerned about it you could always swap them for 773 connectors, that are rated at 32A when in the wago boxes.

Edit: You should also have RCD protection for the circuit.
 
Last edited:
Welcome to the forum mate.
You will be ok with using 222 for extending ring circuits.
If you are concerned about it you could always swap them for 773 connectors, that are rated at 32A when in the wago boxes.

Edit: You should also have RCD protection for the circuit.
Thanks appreciate it! What makes them alright to use to extend a ring is it just that each leg doesn’t car 32A so it is not needed to have one rated at that ?
 
Thanks appreciate it! What makes them alright to use to extend a ring is it just that each leg doesn’t car 32A so it is not needed to have one rated at that ?

Pretty much so.
Does the circuit have RCD protection?
 
Thanks appreciate it! What makes them alright to use to extend a ring is it just that each leg doesn’t car 32A so it is not needed to have one rated at that ?
The only reg for ring final circuits talks about the current carrying capacity of the cable being not less than 20 amps, and the load current in any part of the circuit not exceeding the cable's capacity for any long periods (paraphrasing wildly).

In other words, 20A is in fact the minimum rating. (see reg 433.1.204 for the whole delightful text)
 
Just make sure you use a wago box for each leg and not have all four legs in one box as per wago's instructions
Is that an actual regulation or just because it’s too much of a squeeze?

I’ve extended rfc with a joint in back of socket box. Same thing, isn’t it?
 
Just make sure you use a wago box for each leg and not have all four legs in one box as per wago's instructions

I'm interested in where this nugget is too.

The maintenance free instructions for Wagobox clearly instruct you to reduce the maximum current for the terminals and also the maximum aggregate current which they state is the number of phase conductors * OCPD rating but they also say there are some situations where this may not be the case. I've taken that to suggest that as the maximum current in an RFC is limited to 32A it's within the 50A aggregate limit and therefore it's acceptable to put both joins in one box.
 
I'm interested in where this nugget is too.

The maintenance free instructions for Wagobox clearly instruct you to reduce the maximum current for the terminals and also the maximum aggregate current which they state is the number of phase conductors * OCPD rating but they also say there are some situations where this may not be the case. I've taken that to suggest that as the maximum current in an RFC is limited to 32A it's within the 50A aggregate limit and therefore it's acceptable to put both joins in one box.
If you watch this and then do the calculations a 32a supply will take it well over the 50a aggregate
 
Where is the pic with 4 legs going into box? Again watch the vid and do the calc.

It's not in the video... I was commenting about the documentation by Connexbox....

[ElectriciansForums.net] Extending ring main with wago 222
 
Just make sure you use a wago box for each leg and not have all four legs in one box as per wago's instructions
My bad......Think i wrote this and confused things...What i mean is a Wago box for each leg of the ring ( 2 cables) as per wago's instructions. Not both legs meaning 4 cables in the same box
 

Reply to Extending ring main with wago 222 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I would use the Switch & Load 16A - https://www.quickwire.co.uk/product/switch-load-16a/ Designed to do the same thing as the ceiling rose in...
Replies
5
Views
774
An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
666

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top