smithdarr

Hi,

I'm after a bit of advice on fitting a consumer unit to new extension. The existing house C.U is a 6 way Wylex 100A (non-RCD protected with 2 rings and 2 lighting circuits) with two spare ways. I was hoping to use a 63A MCB in one of the spare ways to feed a new C.U(via earthed metal conduit) in the extension which is to be a kitchen/Diner. From the new C.U I am feeding a cooker circuit, ring, lighting x2, heat/smoke detectors and a feed to a shed. However, it seems you can only get a maximum 40A mcbs for single phase boards and I would presume, even with diversity applied this wouldn'nt be large enough to feed a seperate C.U with a cooker circuit and ring etc. I was looking to use a dual 63a RCD board in the extension and the reason that I'm not just replacing the old C.U is that its current location is not very accessible.
P.s There is 63A RCD shower enclosure fed from supply side of the existing C.U.
Any suggestions of a better way of going about this would be much.appreciated.
Cheers.
 
Is it your property or a clients? I would SUGGEST a new board. If it's not accesible to go in the same place what about changing the tails to longer ones and extending the cables to a convenient place? Unfortunately a job like this has so many variables , without seeing it , it's really difficult to offer any definitive advice. If there's anything specific I or anyone else can maybe help with please feel free...
 
I agree, replacing the existing board would be best. Ideally you should run the new circuits back to the exisiting board (once changed) unless it's going to be totally seperate to the rest of the house.
 

Reply to Extension Consumer Unit in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Replies
31
Views
2K
  • Question
Yep, that’s what I do. That spare RCD has always come in handy down the line.
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top