Hi all.
Looking for opinions on here.
I’ve identified during an eicr that a dry rise pipe used for firefighters in the building is in fact an extraneous conductive part and that it is not bonded back to the MET.
However what I’m questioning is it’s accessability to be touched in the event of a fault.
Pipework is installed in boxing with a key for an access panel for the riser water inlet to be used for the firefighters.
Only person with access is the building manager.
What’s people’s opinions does it require protective bonding or is it deemed not accessible to touch and that’s the end of the matter?
It’s worth pointing out bs 7671 doesn’t mention the fact it needs to be accessible however it’s common sense that says it needs to be if your going to be in contact during a fault between say an exposed conductive part and said pipework.
Thanks

To add the dry riser pipe comes up from the floor in metal and is separate from the cold water pipe entering the building in plastic.
A completely different service it seems.
 
Last edited:
No it means there’s little to no resistance between them or little to no resistance between the source of earthing and the metallic pipe which is introducing an earth potential.
If it was higher than say 23Kohms then I’d consider the pipework as not being extraneous.
There’s no such maximum resistance between bonded parts. 0.05 ohms is a value from GN3 which determines that testing between any two points such as metallic pipes can be considered reliably earthed/bonded
Have you not just said the same as me, but in a more convoluted manner?
 
Extraneous conductive parts are considered as water, Gas, Oil, fire fighting pipework in high rise blocks, or large buildings, lightning conductors, structural steelework etc, ie they do not form part of an electrical installation
Seriously?
Are you telling me you are unaware of the purpose of Main Equipotential or Protective Bonding conductors?
 
Have you not just said the same as me, but in a more convoluted manner?
No not really.
It indicates that the metallic pipe is in contact with earth but as I’ve said, it’s not connected to the MET and has no continuity to it when using a wander lead to test it from the MET to the pipework.
The test I’ve done says to me it’s extraneous as it has a very low resistance to earth.
If it was connected to the MET then I’d have continuity.
Also the IR test I did was with the earthing conductor disconnected from the source of earthing and the test made between metallic pipe and the DNO source earth.
TN-S in this case on the side of the 3 phase Lucy unit with the earthing bolt.
 
No I just wanted you to explain your statement, it seems we are getting mixed up here Spin, of course I know the reason, it was just I thought your statement was a bit far reaching. And why you feel the vids are misinforming people that's all.
 
Last edited:
No not really.
It indicates that the metallic pipe is in contact with earth but as I’ve said, it’s not connected to the MET and has no continuity to it when using a wander lead to test it from the MET to the pipework.
The test I’ve done says to me it’s extraneous as it has a very low resistance to earth.
If it was connected to the MET then I’d have continuity
No, it does not indicate that metallic pipe is connected to earth. It indicates that there is a reliable connection between the metallic pipe and the MET.

Your second posts states: you have zero resistance between the metallic pipe and the MET and no continuity between the metallic pipe and a known earth.
Now you appear to be saying the opposite.
Please clarify.
 
No, it does not indicate that metallic pipe is connected to earth. It indicates that there is a reliable connection between the metallic pipe and the MET.

Your second posts states: you have zero resistance between the metallic pipe and the MET and no continuity between the metallic pipe and a known earth.
Now you appear to be saying the opposite.
Please clarify.
Right there’s no continuity between MET and pipe when carrying out a continuity test.
There a reading of 0.00 Mohms between the source of earth to the installation (not at the MET as I disconnected it doing the IR test).
Conclusion is that the metallic pipe is in good contact with earth(externally) and is extraneous but it is NOT connected to the buildings earthing.
Got it??
 
Right there’s no continuity between MET and pipe when carrying out a continuity test.
There a reading of 0.00 Mohms between the source of earth to the installation (not at the MET as I disconnected it doing the IR test).
Conclusion is that the metallic pipe is in good contact with earth(externally) and is extraneous but it is NOT connected to the buildings earthing.
Got it??
I have thanks
 
So why did you say this:
Testing from the MET or rather the source of earthing to said pipe.
Main earthing conductor disconnected from source earth
IR set to 500v reading of 0.00 Mohms
Also no continuity between said pipework and a known earth source
If you tested IR between the MET (with the Main earthing conductor disconnected) and the pipe, to obtain a reading of 0.00 Mohms, that would indicate a reliable connection between the pipe and the MET.
To then state there is no continuity between said pipe work and a known earth source, would indicate no connection to earth.
Are you now saying, you did not test IR between the MET and the pipe, that in fact you tested between the Earthing conductor and the pipe?
If so what does the statement that there is “also no continuity between said pipework and a known earth source” mean?
 
So why did you say this:

If you tested IR between the MET (with the Main earthing conductor disconnected) and the pipe, to obtain a reading of 0.00 Mohms, that would indicate a reliable connection between the pipe and the MET.
To then state there is no continuity between said pipe work and a known earth source, would indicate no connection to earth.
Are you now saying, you did not test IR between the MET and the pipe, that in fact you tested between the Earthing conductor and the pipe?
If so what does the statement that there is “also no continuity between said pipework and a known earth source” mean?
The source of earthing is what the DNO provide for the installation.
A known earth source is exactly that, a point in the installation such as the MET that’s connected to the earthing arrangement in the building.
My 2nd post in the thread is clear enough.
Testing the metallic pipe was done in accordance with gn8 pages 74 and 75.
Testing between earth and the suspect pipework using an insulation resistance tester set at 500 volts D.C. and the reading being less than 22Kohms or as displayed on my instrument 0.00 Mohms.
Have a read up on it why don’t you?
 
Last edited:
Guys im confused. If you wanted to know if a pipe or say tap could have a potential difference. What tests would you do? What results would you expect? You'll have to make the answer simple as im still just a trainee
Check out pete’s uploaded videos.
Generally the formula is 230/0.01 amps (10mA being the let go threshold)
To assess whether Earth potential is liable to be introduced by a conductive part that is connected to the general mass of Earth through a resistance, a measurement should be made of the resistance between the conductive part and the main earthing terminal of the installation.
As generally our continuity meters won’t read that high say (22Kohms) then an insulation resistance meter is used set to 500v D.C. and a measurement is taken between the suspect pipework and the earth arrangement to the installation.
Also For a better technical explanation check out gn8.
 
Last edited:
The discussion isn’t or isn’t it extraneous , it’s if it’s accessible in the sense that it requires bonding and it probably should.
Bet you are glad you asked now:D
I think you have to say it is accessible, amen.
 

Reply to Extraneous conductive parts in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi I need help with understand supplementary bonding. I know RCD is additional protection and in the even of the fault at leakage of 30mA, it...
Replies
0
Views
45
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top