Darkwood
I had a customer with a commercial kitchen and she received a shock as she bridged 2 tables, now both tables past the 22k to met test but a metal appliance had earthed one of the tables and a seperate fault had put a voltage into the table which had no real path through her until she bridged the tables, the fault was on a damaged fridge flex laying in a spillage which had tracked into the table - this presents a situation like previously mentioned that although the tables met requirements not to be bonded the owner had introduced an inderict connection to the MET. I find myself questioning the relaxation of the regs especially on situations where the installation isnt covered by and rcd, by the way i replaced the fuseboard and left tables unbonded as the rcd would have seen the damaged cable and i cant see this been a potential hazard in future.