i am about to build a partition wall in my daughters house to split one big bedroom into 2 for my grandchildren. Iam going to install 2 double sockets on each side of the new wall. There is one double socket in the bedroom at present and my intent is to split the ring under this socket by cutting one of the cables and inserting the new cable run via 2 30a junction boxes. When i polled up the floorboard yesterday I was surprised to see only 1 set of connections to the socket via a single cable. I confirmed this by opening the face plate and confirming there was only 1 set of connections. This indicates that the socket is a spur which is very surprising as it is the only socket in the room. Obviously I cannot run the new cable run from a spur. Am i missing something here?,
 
If its entered under "Other Work" as I was advised(incorrectly?) to do (for the last 3 years) then it appears as......Notifiable but i will them ring tomorrow

Of course they'll say it's notifiable- they want the money!!
 
who is going to check zs, volt drop, continuity,polarity,insulation resistance,rcd protection present and tested and bonding?
an electrician should do these tests without thinking about it, anyone could add extra sockets and yes they should work if done corectly the problem is always if a fault occured later on you see dead people.
i think but not sure its a minnor works cert but not notifiable unless in special location.
this does not mean anyone can do this work, they should still be competant and do tests listed on minnor works it's up to diyer to prove competancy later on if someone dies.
I would also ask if anyone knows of any household insurers that have not paid out because of diyers?
 
again thankyou all for your comments all of which i hear and take on board. What i would like to first do is establish if i have a ring or radial circuit. it is wired as follows
sockets excluding cooker are fed via 1 rcd rated at 32a
sockets in bedroom 1 and 2 have 2 sets of connections to each
single socket in bedroom 3 has 1 set of connections to it
this tells ne it is a radial circuit which i find very surprising
would someone please confirm or otherwise my thinking on this
 
i am about to build a partition wall in my daughters house to split one big bedroom into 2 for my grandchildren. Iam going to install 2 double sockets on each side of the new wall. There is one double socket in the bedroom at present and my intent is to split the ring under this socket by cutting one of the cables and inserting the new cable run via 2 30a junction boxes. When i polled up the floorboard yesterday I was surprised to see only 1 set of connections to the socket via a single cable. I confirmed this by opening the face plate and confirming there was only 1 set of connections. This indicates that the socket is a spur which is very surprising as it is the only socket in the room. Obviously I cannot run the new cable run from a spur. Am i missing something here?,

Without testing the continuity of the circuit I wouldn't dare suggest anything regarding it, best to leave well alone unless you feel you can do it correctly, remember your Grandchildren will be using these sockets, do you want to be responsible for their safety regarding this? Not trying to be awkward, I wish you well, but cannot help you do the Job yourelf due to your post, I hope you have a nice 2013 by the way.


Mike
 
good question
who is going to check zs, volt drop, continuity,polarity,insulation resistance,rcd protection present and tested and bonding?
an electrician should do these tests without thinking about it, anyone could add extra sockets and yes they should work if done corectly the problem is always if a fault occured later on you see dead people.
i think but not sure its a minnor works cert but not notifiable unless in special location.
this does not mean anyone can do this work, they should still be competant and do tests listed on minnor works it's up to diyer to prove competancy later on if someone dies.
I would also ask if anyone knows of any household insurers that have not paid out because of diyers?
 
again thankyou all for your comments all of which i hear and take on board. What i would like to first do is establish if i have a ring or radial circuit. it is wired as follows
sockets excluding cooker are fed via 1 rcd rated at 32a
sockets in bedroom 1 and 2 have 2 sets of connections to each
single socket in bedroom 3 has 1 set of connections to it
this tells ne it is a radial circuit which i find very surprising
would someone please confirm or otherwise my thinking on this

Clearly not!
 
again thankyou all for your comments all of which i hear and take on board. What i would like to first do is establish if i have a ring or radial circuit. it is wired as follows
sockets excluding cooker are fed via 1 rcd rated at 32a
sockets in bedroom 1 and 2 have 2 sets of connections to each
single socket in bedroom 3 has 1 set of connections to it
this tells ne it is a radial circuit which i find very surprising
would someone please confirm or otherwise my thinking on this

Firstly it is not possible to tell visually if a circuit is a radial or ring without actually tracing the path of the wires....you will need to test to confirm. If the circuit is protected by a 32a MCB...(not RCD??...hope this is a typo?)...then it may be a ring,as a radial will normally be protected by a 20a MCB. But as already stated only testing can confirm whether the circuit is a ring and hence how it should be altered.
The job as you describe it is NOT notifyable to LABC....but still comes under the umbrella of part P and so must be carried out in accordance with bs7671 or you are breaking the law. If you are competant to do it to 7671 then go ahead,there is no restriction on DIY electrics as long as part P is complied with.
 
What the !!!! sort of question is this, don't you know how to check out cabling to and from sockets etc lol
again thankyou all for your comments all of which i hear and take on board. What i would like to first do is establish if i have a ring or radial circuit. it is wired as follows
sockets excluding cooker are fed via 1 rcd rated at 32a
sockets in bedroom 1 and 2 have 2 sets of connections to each
single socket in bedroom 3 has 1 set of connections to it
this tells ne it is a radial circuit which i find very surprising
would someone please confirm or otherwise my thinking on this
 
Wouldn't he be better off getting a spark to do the job ?
Firstly it is not possible to tell visually if a circuit is a radial or ring without actually tracing the path of the wires....you will need to test to confirm. If the circuit is protected by a 32a MCB...(not RCD...hope this is a typo?)...then it may be a ring,as a radial will normally be protected by a 20a MCB. But as already stated only testing can confirm whether the circuit is a ring and hence how it should be altered.
The job as you describe it is NOT notifyable to LABC....but still comes under the umbrella of part P and so must be carried out in accordance with bs7671 or you are breaking the law. If you are competant to do it to 7671 then go ahead,there is no restriction on DIY electrics as long as part P is complied with.
 
To be honest Rock, I am starting to think, that Part P, should just be totally ignored.
I had someone tell me the other day, that you must have the 2391 to be able to issue an EIC or MEIWC, or be a member of a competent persons scheme.
Apparently this bit in Part P says so:
1.10 “Qualified” in this context means having
the appropriate qualifications, knowledge and
experience to carry out the inspection and testing
procedures and complete the relevant electrical
installation certificate.



Like most DIYers who don't know anything about Part P
 
Wobblymike is in my neck of the woods. Send me a private message if you want the job done safely and correct. This will not cost you a fortune and its a small price to pay in the long run.

Ps the price will go up by 20% if your a Wakefield Wildcat fan lol.
 
He should't be touching the electrical installation if he's not a spark
probably...but that wasnt what he was asking,i answered his question. Tbh if thats the forum policy we might as well just answer every thread not started by an electrician...."get an electrician in" and not bother with any other advice.
 

Reply to exyending ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
As long as you can carry out all the necessary testing, certification, are insured to do the work and all is carried out to Amendment 2 of the regs
Replies
1
Views
564
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
407
  • Question
Why aren't you asking them?
Replies
5
Views
784
Yes, you run each socket as a point to point connection, and use a switch (it doesn't need to be PoE unless you are wanting to power devices via...
Replies
6
Views
602
  • Question
Thanks for the advice.
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks