On my fans and controllers they had 2 x extra connections, labelled TK on controller and TB on fan, both were for thermal cut out!

I stand corrected - not seen that. I guess the reset is in the controller then? What make of fan?
TK is standard for thermal cutout (thermistor). The TK terminals are designed to be connected to the control side of the DOL starter. They're NOT designed to have the motor run current going through them. Systemair is one European company that uses this system and possibly from memory EBM Papst on their external rotor motor range of fans.
 
TK is standard for thermal cutout (thermistor). The TK terminals are designed to be connected to the control side of the DOL starter. They're NOT designed to have the motor run current going through them. Systemair is one European company that uses this system and possibly from memory EBM Papst on their external rotor motor range of fans.

It was a systemair controller. Live,neutral and earth to live, neutral and earth of fan. 2 x TK terminals on controller which I connected to the only other 2 connections at the fan marked TB. Is this not correct?
The guys working for the firm that supplied the system and were doing the associated ducting said that was the way to do it.
 
i wired a few Sp fans lately with electronic speed control

3-core to fan and thermal overload integral to fan

electronic speed control has to be reset in event of overload

some fan's will have overload wired into external control cct
 
The boss of company that supplied the fans drew a simple wiring diagram which showed 5 cores from controller to fan, 2 marked TK.
 
Systemair have a CDRom catalogue which has a fan selection program on it called Systemair SP.exe. In the program they give you wiring drawngs for every fan they make as well as specs for currents, voltages, cap sizes etc etc. I'm not sure if it's available on their website but any Systemair agent should give you a copy for free if you ask them. Same goes for Ziehl, Elta, Woods, Howden Donkin, Vent Axia and EBM Papst.
 
okay got two more of these fans too wire up with speed controllers and another 2 later in the week, these are the connections,

from Z on controller to P on Fan
from U on controller to U on Fan
and UZ on controller to K on Fan

What colour cores would you normally use in this situation, Also which would be your live and neutral had one this week where the site electrician had wired a 4 core cable from the speed controller up to a 4 pole rotary isolator in the loft, and to feed the fan from this used only the brown and blue cores as live and neutral leaving out the black and grey, cant understand why this was done.

Hope this is clear if not just ask me i wana get this sorted properly we have different views at work,
 
Does anyone know what i can do in this situation.. Got 2 ceiling fans (commercial fans, not extractor) to put up and the supply cable is 1.5 T&E- these types of fans need max 3A fused isolator normally-all i have is a 1 gang 1 way switch which i think was supposed to switch fans on / off. These fans have a 4 wire control unit with them and i obviously only have the T&E.

I think i know the answer... New supply for fans but that will cause some major damage to the fresh plaster.. ?
 
Does anyone know what i can do in this situation.. Got 2 ceiling fans (commercial fans, not extractor) to put up and the supply cable is 1.5 T&E- these types of fans need max 3A fused isolator normally-all i have is a 1 gang 1 way switch which i think was supposed to switch fans on / off. These fans have a 4 wire control unit with them and i obviously only have the T&E.

I think i know the answer... New supply for fans but that will cause some major damage to the fresh plaster.. ?
What does the "4 wire control unit" require? Would need more information to give a useful answer.
If it is permanent line, switched line, neutral and earth then presumably there is a timer or other function; this would not be usable but change the switch for an SFCU, and you have an on off fan, done. (probably would have been better to start a new post!)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
fans and speed controllers
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
26

Advert

Thread statistics

Created
Sparky_Ben,
Last reply from
Richard Burns,
Replies
26
Views
10,257

Advert

Back
Top