Got a call to a farm today. The usual thing all barns and sheds fed overhead and TT'd. The Farmer said he and his livestock wer getting shocks during milking.
On arrival initialy found the only RCD in the place (feeding 4 barns and the milking parlour) was u/s.
I replaced this but testing the new 100A 100ma RCD it failed to trip on the 5x setting??
It was ok on the 1/2 and 1x test but not the 5x??? Has anyone seen this before.
Anyway it reset and held until I switched on the lights in the Milking parlour then tripped. I fixed the fault in one of the lights then all was well. Also replaced a 13a S/O with no earth with a RCD item and ran in new earth.
Any feedback on the RCD prob would be appreciated