Inspired from the "show us your installs" thread, Trev has come up with a great idea..... Lets find the faults.

Here is the first one:-

698.jpg

Loads of faults in that picture! How many can you see?

BTW yes that is SWA at the bottom lol.
 
No gland on the SWA, No sleeving on the T&E CPC, unidentified terminations on the SWA, Exposed copper on all terminations. T&E used outside, not fit for the environment it is installed.

The armour of the SWA may be earthed at the other end but i really doubt it. The cut off grey core if not being used should be connected to earth.

I am sure there is more so be interesting to see what others come up with :smile:
 
No front plate but that's off for us to look at it

Far far too much conductor showing, needs cutting back
 
The SWA is not earthed at the other end btw.

What about IP protection???
 
Just read your PM Paul! Doh! Ooh incorrect glands (for both types of cable), unnecessary hole in the back of the box, top entry into box which probably could have been avoided, reverse polarity, no sleeving on CPC, no identification sleeving, bare conductors aaaand possibly connector block too small, I reckon 15A and looks like a 6mm T&E and 4mm SWA but could be wrong! Not to mention no IP rating, especially with no lid ;)
 
Other than the fact that the T&E sheath makes it into the box, I can't see anything RIGHT with this...

I reckon I came too late to this party to improve on the answers... :)
 
Other than the fact that the T&E sheath makes it into the box, I can't see anything RIGHT with this...

I reckon I came too late to this party to improve on the answers... :)

Yep looks like I'm late too... have read all the answers above and tbh is not much left to add on :)
That box is disaster waiting to hapen:)
 
I'm sure I answered this around 2 hours ago but it's not showing up? :(

Yes mate you did, I moved the picture onto this new thread to keep it away from the weekly question thread, pity you saw the thread first and not your PM.

Resu you were correct as per normal :smile: I'll try and post up some more, looks like you lot enjoy these.
 
I am pretty sure there is no reg against this as long as the conductors are properly identified at every connection. (so my comment of unidentified conductors covered that).

I would be happy to be corrected on this though.

To add, any trained person would not have done it as the picture shows as this is clearly DIY gone wrong.

how come no one has mentioned using the brown as cpc on the swa?


red - red
black - black
blue - bits

lol
 
Last edited:
Is the PVC cable secured to the wall? To avoid mechanical stress as well? (housekeeping to say the least) just to add. :X risk assessment : hazard electric shock, risk certain.
 
Re IP rating, it looks remarkably dry in there!
Paul, stop posting pictures of your dodgy work and fishing for advice on how to correct it. :-)
 
Re IP rating, it looks remarkably dry in there!
Paul, stop posting pictures of your dodgy work and fishing for advice on how to correct it. :-)

All that is needed is to wrap some electrical tape around the terminal block and silicone a butter tub lid over the top????

Really good to see you in here Archey. Need someone just as bonkers as me around :20::20::20:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fault find #1
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
Paul.M,
Last reply from
Paul.M,
Replies
21
Views
360

Advert

Back
Top