110v from switch to switch (see attached picture), tn-cs system with 30mA RCD in Place, trips fine when tested at 100% and 500% customer complained of getting shocked when touching both switches at once but doesn’t trip with this fault, have a few theories, but any suggestions?

514258D2-9701-4C38-8195-170B5A64DE7A.jpeg
 
Possible poor or no earth at one of those switches, therefore creating a potential difference. Chances are it’ll be the light switch that isn’t earthed properly as there’s more connections throughout the circuit to come loose.
 
I haven’t had a chance to do any tests yet apart from very quickly testing the rcd, with the customer away im not going asap I’m going to get there this week at some point, what’s concerning me is why the rcd never tripped? As even if there was a loose earth connection, or no earth atall surely the rcd should still of picked up an imbalance between live and neutral and tripped regardless when the customer touched the switches?
 
I had similar ages ago, customer getting intermittent tingles from metal dimmer switch, no voltage between plate & known earth mind.

I left her to fry, whilst consulting members here (nahh not really, swapped switch to plastic). Went back to investigate with new advice and found there was no continuity between installed switch cpc & earth terminal in CU.
 
I haven’t had a chance to do any tests yet apart from very quickly testing the rcd, with the customer away im not going asap I’m going to get there this week at some point, what’s concerning me is why the rcd never tripped? As even if there was a loose earth connection, or no earth atall surely the rcd should still of picked up an imbalance between live and neutral and tripped regardless when the customer touched the switches?

Just shows why you shouldn't have an over reliance on RCD's. Guess the flow through her etc to Earth, was enough to give a tingle, insufficient for imbalance. Dunno, forum boffins will say.
 
I'd suspect that the earth connection somewhere is missing (as mentioned probably on the lighting circuit) and you have a low Insulation resistance between L&E. If so, your need to check the whole circuit thoroughly as you have no idea where the fault is. The CPC could be broken to the first light in the circuit and other metal light fittings and accessiores may potentially be live too !
As RCDs only work on earth imbalance maybe the touch current was below 30mA it may have been different if the customer was bare foot on a damp floor either way this is a potential killer.

I' be carryng out continuity and IR tests the breaking down circuits, at a guess you find a snapped CPC and a squashed Live somewhere on one of those two circuits.
 
Last edited:
I haven’t had a chance to do any tests yet apart from very quickly testing the rcd, with the customer away im not going asap I’m going to get there this week at some point, what’s concerning me is why the rcd never tripped? As even if there was a loose earth connection, or no earth atall surely the rcd should still of picked up an imbalance between live and neutral and tripped regardless when the customer touched the switches?

Maybe time to review how rcd's work ...
 
Capacitive coupling or inductance between the earth and other cables can be enough to measure 100v and feel a tingle. But if you measured the current discharged it would be tiny. Switch mode PSUs tend to have a bit of earth leakage which will often appear as half mains voltage if they aren't properly earthed.

So first port of call should probably be earth loop impedance test at switch/earth continuity test.
 

Reply to Fault on domestic home wiring in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

Long shot, but looking at the previous posts. hope i have understood correctly. 1. continuity between live and earth 2. no continuity between...
Replies
6
Views
1K
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
773

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top