The capacitor can be tested for o/c or s/c, my preferred method is using an analogue ohm meter..
Failure of the capacitor will lead to the early demise of the ballast..
Yes across the lampholder terminals, you should read the same voltage to what the lamp is rated..
Current reading will be in excess of 10amps not by much though probably between 10 and 12ish..

Before removing any components for replacement, testing, etc please discharge the capacitor..

if you have time familiarise yourself with the healthy floodlight, taking notes of test voltages, etc.
 

Reply to Fault on three phase sports floodlighting in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top