went to work today, on a hospital we’ve been working atand we got there and a phase of works that we’ve have already done I tested itan powered it up last week, the lights were all flickering and one light sw onone circuit was switching another light on another circuit very strange, I tookthe db lid of then checked voltages I got L1-N 400 L2-N 230, L3-N 69v,
even neutral earth 230v, so I immediately turned the full db off faults didn'tdisappear, went down to section board it was an old proteus fitted in the1970's,,we used a spare way on it to feed the new db checked the voltages antthat they were fine,, so I took some loop reading l-n l-e l-e was fine l-n werehigh and unstable to I’m thinking loose neutral I turned off and on thesw a few times put contact grease n the fault cleared all is good,,,but whydid I get 400v down l-n is it due to an unbalanced load trying to balance itsself, and finding an alternative root back to the source via another phase anwhy did the rcbo not trip,,,rcbo only has neutral tail no earth,,,id reallyappreciate people opinions on this took me 3 hours of scratching my head onthis


 
Classic symptoms of lost neutral, should only have cost about one second of head-scratching! Yes, the different P-N voltages occur due to the imbalance of load currents, the difference of which would be the neutral current under normal circumstances. Make sure you really did find the fault as lost neutrals can wreak havoc, set things on fire, destroy valuable pieces of kit, cause major insurance claims!

Why would you expect the RCBO to trip? There's nothing specifically to cause overload (although it could happen when things are overrun/damaged) and nothing leaks to earth.
 
Classic symptoms of lost neutral, should only have cost about one second of head-scratching! Yes, the different P-N voltages occur due to the imbalance of load currents, the difference of which would be the neutral current under normal circumstances. Make sure you really did find the fault as lost neutrals can wreak havoc, set things on fire, destroy valuable pieces of kit, cause major insurance claims!

Why would you expect the RCBO to trip? There's nothing specifically to cause overload (although it could happen when things are overrun/damaged) and nothing leaks to earth.

I think the cause was a sw fuse on the old section panel,, the sw fuse has never been used and is from the 1970's so I think it was just poor contacts,,, once it was turned on and off a few times the fault cleard,, how else can I ensure that was the cause ive never come across the fault before ive been doing the job for 9 years now always learning
 
Bull in a china shop fault finding that is. If you are fortunate enough to have it under fault condition in front of you, be methodical and treat with kid gloves. Otherwise you will be guessing.
 
I think the cause was a sw fuse on the old section panel,, the sw fuse has never been used and is from the 1970's so I think it was just poor contacts,,,
Given the cost implications to the customer with this type of fault I'd suggest removing, stripping and overhauling the switch fuse or replacing it entirely with a new item. A floating neutral could cost tens of thousands in damage to equipment quite easily in a hospital....if not more.... so I wouldn't take the chance that switching it on and off a few times has ensured it won't reoccur.
 
Given the cost implications to the customer with this type of fault I'd suggest removing, stripping and overhauling the switch fuse or replacing it entirely with a new item. A floating neutral could cost tens of thousands in damage to equipment quite easily in a hospital....if not more.... so I wouldn't take the chance that switching it on and off a few times has ensured it won't reoccur.

why did this have to happen on my job, ive go five other conections to make on to this sction panel,,to remove the sw fuse would be no easy task
 
Lol, I'm not sure what to say really, **** happens. Maybe make a report for the client with a quotation and highlight the risks involved with the high likelyhood of equipment damage and leave the ball in their court plus you cover yourself that way.
 
if my l-n loop reading are coming back at 0.05 on all phases would u say that's a safe bet the fault has cleared
A better test would be to monitor the voltdrop across the contacts when it under a decent load or preferrably full load but like I say I'm not usually a gambling man when it comes to hospital equipment ;)
 
I am trying to help you mate. Let them know and then sleep easy that they are aware. You did not create the problem, but you found it, so advise and then go from there.
 

Reply to fault today at work 400v live to neutral in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
407
T
  • Question
Very informative and helpful. I would have thought that the real intended purpose was to make money.
2
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top