Tris Zanker
Been called to a fault today customer saying RCD tripping when under load.
I go rcd holds in till he plugs something in that say uses more that 50w, I try and ramp test rcd - no trip, 5x no trip, 1x no trip, rcd test bottom - no trip. so I think it’s a faulty rcd, i put a new rcd in and test again 5x no trip, 1x no trip, rcd test bottom - no trip same thing again as soon as he plugs something with some load in it trips the new rcd out.
I look in to it a bit deeper IR on all circuits >20M.
I then disconnect the main earth from the PME, everything is then fine, RCD trips correctly and stays on under load, I've now decide it's done to the DNO so out comes western power they that one look and say nope it’s on your side it must be a faulty appliance.
In the mean time I’ve replaced the consumer units Main switch with an RCD due to the property having unstable earth.
Any ideas as to where i can go from here as it’s something I’ve never came across before?
I go rcd holds in till he plugs something in that say uses more that 50w, I try and ramp test rcd - no trip, 5x no trip, 1x no trip, rcd test bottom - no trip. so I think it’s a faulty rcd, i put a new rcd in and test again 5x no trip, 1x no trip, rcd test bottom - no trip same thing again as soon as he plugs something with some load in it trips the new rcd out.
I look in to it a bit deeper IR on all circuits >20M.
I then disconnect the main earth from the PME, everything is then fine, RCD trips correctly and stays on under load, I've now decide it's done to the DNO so out comes western power they that one look and say nope it’s on your side it must be a faulty appliance.
In the mean time I’ve replaced the consumer units Main switch with an RCD due to the property having unstable earth.
Any ideas as to where i can go from here as it’s something I’ve never came across before?