identify 3 possible defects that could be identified during the inspection process on a distribution board.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss faults on Distribution board in the Talk Electrician area at ElectriciansForums.net
where does trhat come from?try this. minimum size of cpc able to carry fault current of 150 A. Disconnection time of 0.4 seconds. i make it 0.68mm.
Reply to faults on Distribution board in the Talk Electrician area at ElectriciansForums.net