Had 16 Sanyo 250watt HIT panels with Sunnyboy 4000TL inverter installed last week, was working okay for first day but since then getting numerous Grid faults which sometimes throws up Fault-call installer.

Just wondered if it is likely I have a faulty Inverter or would it be something to do with the grid, had power showing zero sometimes without any warnings.

I have informed installer, waiting for electrician to contact me but thought I would see what problems any others have had.

I have Sunny Explorer running but I am afraid most of the readings mean little to me and the help pages aren't great, or maybe it is just me...
 
Hi Richard,

1. do you have the installation manual, this will show all the fault codes and the reasons for them?
2. Is the system grid connected or off grid? do you have an unstable grid supply?
3. just a note: the installer has oversized your inverter! this is not an issue it means you have just had to pay a little more where its not required, if the inverter needs changing maybe suggest to your installer a SB3300, and maybe the couple of hundred quid back :smile:
 
Hi Richard,&nbsp;<br><br>1. do you have the installation manual, this will show all the fault codes and the reasons for them?&nbsp;<br>2. Is the system grid connected or off grid? do you have an unstable grid supply?<br>3. just a note: the installer has oversized your inverter! this is not an issue it means you have just had to pay a little more where its not required, if the inverter needs changing maybe suggest to your installer a SB3300, and maybe the couple of hundred quid back&nbsp;<img src="http://www.electriciansforums.net/images/smilies/smile.gif" border="0" alt="" title="Smile" smilieid="294" class="inlineimg">
 
Hi Martin, thanks for reply, unfortunately there aren't any fault codes showing, only says Grid disturbance restarting in ** seconds, the red triangle is showing and says fault though.
The system is grid connected and I am not aware of any problems with supply.

Yes I thought the inverter was oversized but as I wanted a TL model from what I have read on here, rightly or wrongly, and the whole package price was very competitive.

Having just looked on Sunny Design about cable runs, I notice that I have a long (20m) AC run from inverter to CU as this looks like only 2.5mm cable wondered if this may be a problem? :(
 
Richchad,

this could be your issue, does the system behave in low light (i.e low output)?

the maximum AC current output of the 4000TL is 22A, BS7671 will tell you that the maximum current carrying capacity of 2.5mm cable is 20A, 4mm will give you 26A. is the cable getting warm when it cuts out?

hopefully your installer should sort this out for you?? Time is Money :smile:
 
This will be an issue your installer needs to put right and you should have contacted them first. 4000TL Needs a 6mm cable as a minimum. All of the docs can be downloaded from sma.de

Also get your hands on a bluetooth dongle for your computer and download sunnyexplorer from the above site. You will then be able to download the fault history from the inverter (assuming its setup correctly!) Just read you have this.....

Stick with the 4000TL, nothing wrong with it. The 3300 has a slightly lower efficiency for the setup, so your installer got that bit right. Only has a single input and dont think its bluetoothed as standard.
 
Last edited by a moderator:
Yes, it seems okay first thing, ie low light but trips when getting brighter, have had over 15 fault events showing today, clears and trips almost immediately again, haven't felt the cable, but will do.

I spoke to my contact with the company and mentioned about the cable, he said the electrician would have installed 4 or 6mm cable, but having looked at it, it sure looks like 2.5mm. He was going to speak to electrician.

Waiting for them to come back to me..........
 
Just felt the cable, doesn't feel hot but I guess as system hasn't been producing any power for the last 4-5 hours, as it trips after resetting, it hasn't had chance to get warm..
4 or 6mm cable would look much larger that 2.5mm twin & earth wouldn't it?

Hi Graeme, I have the sunny Explorer running on my laptop, waiting for delivery of bluetooth dongle for main home PC, i have seen all the fault events but no fault codes showing, only Grid Faults incoming and out going?
 
Deffo need the cable replacing as its 6mm as a MINIMUM for up to 23m

Thanks for that, will ask for it to be replaced with 6mm, well that has given me great faith in the electrical sub contractor they use....! It seems pretty basic knowledge if you are installing PV systems I would have thought, maybe he was just having an off day.........................
 
2.5mm twin and earth and 32a breaker on a SB4000TL? That doesn't fill me with confidence. Have they filled it out as such on the test sheets?

Regarding the SB4000TL, the installer got this right. A perfect inverter for the size system you have. Using the SB3300 would result in yield loss I would suggest.
 

Reply to Faults on new system just installed lastweek in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

  • Question
This is a baffling fault I've been fighting with for a couple of weeks now, so I wondered if another set of eyes will help. I installed an EV...
Replies
0
Views
178
I well remember the sliding windows on ther Mini, and also the manual choke and the foot-operated dip switch. I recently traded in my 18 year old...
    • Like
    • Informative
2
Replies
18
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top