What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by their buttons before starting work.

But on completion of work, one of the RCCDs, when tested via tester, would not trip, the other operated as expected!
 
Test without wiring connected to RCCB
The button was working, but it would not trip in 300ms @ 30mA when I tested it. I've told the client it urgently needs replacing and that they effectively have no RCD on that side of the board and are not currently compliant. Is that me covered? It's not like I have the authority to turn their power off.
 
Test without wiring connected to RCCB

Did you test it with the outgoing circuits isolated from it?
If an RCD won't trip with a circuit connected what is the point of testing it without the outgoing circuit connected you might prove it trips but will it trip under a fault condition when the circuit is connected. I generally find that a ramp test finds the trip exceeds the 30mA threshold and the RCD is faulty
 
Simply to determine whether the RCD is faulty or there is a wiring fault. OP has not provided any more info so we have what we have. RCD trips on button but not with tester, no idea where it is being tested.

I do sometimes wonder why i even bother with replies, this is bread and butter.

I dont "generally" find anything, i have had RCDs blow up in my face when pressing the button, i have had RCDs non functioning because of wiring faults and RCDs that trip when i stamp on the floorboards, lol
 
As others have said, you need to test it with the outgoing terminals disconnected.
If it then trips, it is likely you have a bad fault somewhere. I have had this 3 times now. There is a long thread on it somewhere which @davesparks has given lots of useful information.
 
Thanks for the replies all.
Sorry if this is bread and butter.

I tested from a ring main on that side of the board, the tester ran through the cycle 1/2 and 1/2 at 180, then 1 ran over 300ms and the tester aborted the rest of the tests. At that point, I assumed it was a faulty device. As I say when testing the other side of the board the RCCD operated properly.

So I understand you are telling me to test with the protected circuits disconnected (would turning the MCBs off be sufficient? Or would we need to disconnect from Earth and Neutral bars?) and then test.

If the RCD then operates as expected it's OK, if not it is faulty.

If the RCD is OK, then there is a fault somewhere. So I'd say add circuits back 1 at a time and retest, to identify the faulty circuit.

For my info, what type of fault could stop both the RCCD and the faulty circuits MCB from operating?
 
I have found that a high resistance neutral to earth fault can cause an RCD not to operate. I have also found that a doorbell transformer connected to one of the circuits can cause an RCD not to operate. And of course, a type AC RCD can be blinded by an appliance or other device that happens to be leaking DC current and thus the RCD will not operate.

Guidance Note 3 indicates that the test should be carried out at the RCD with the load disconnected to avoid spurious results.
 
How is this for a procedure? I'd still appreciate some guidance on what to typically look for if it comes to a circuit fault that would give this issue.

"If RCD fails to operate when tested at 30mA, follow the sequence below,

Test with the protected circuits disconnected (MCB turned off)
If the RCD then operates as expected it's OK, then there is a fault somewhere. So add circuits back 1 at a time and retest, to identify the faulty circuit.
Rectify the fault and test again.

IF RCD does not operate, remove neutrals and test again.
If the RCD then operates as expected it's OK, if not it is faulty.

If the RCD does not operate, it is faulty replace.

If the RCD is OK, then there is a fault somewhere. So add circuits back 1 at a time and retest, to identify the faulty circuit.
Rectify the fault and test again."
 
I have found that a high resistance neutral to earth fault can cause an RCD not to operate. I have also found that a doorbell transformer connected to one of the circuits can cause an RCD not to operate. And of course, a type AC RCD can be blinded by an appliance or other device that happens to be leaking DC current and thus the RCD will not operate.

Guidance Note 3 indicates that the test should be carried out at the RCD with the load disconnected to avoid spurious results.
Thanks Loz.
 

Reply to Faulty RCD tripping on the button but not via the tester in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
618
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
702

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top