Hi all, having a problem on a job...
Using a switched FCU to control some LED under-cabinet strip lights. Customer reported that the lights were staying on after the FCU had been switched off. So I thought the FCU must be stuck in on position, so I replaced the unit.
Had a call from the customer today reporting the same problem.
Upon inspecting the original FCU, it appears to be working as it should. I.e. it isolates both live and neutral.

Any ideas?
Thanks in advance.
 
possible. it's quite common for GU10 LEDs to stay faintly lit or flash after switch off. capacitance or induced voltage from adjacent live cables. a snubber draians the unwanted voltage away.
 
try a 1 watt resistor, value around the 200Ω mark across the ELV feed to the strip
 
Hi all, having a problem on a job...
Using a switched FCU to control some LED under-cabinet strip lights. Customer reported that the lights were staying on after the FCU had been switched off. So I thought the FCU must be stuck in on position, so I replaced the unit.
Had a call from the customer today reporting the same problem.
Upon inspecting the original FCU, it appears to be working as it should. I.e. it isolates both live and neutral.

Any ideas?
Thanks in advance.

My idea is that it may have been wise to test the suspected "faulty" FCU BEFORE you went to the trouble and expense of replacing it. ;)
 
To Geordie Spark: I had this problem with an FCU before, admittedly an LAP one. So thought it would be prudent to take a replacement with me and just swap it.
The FCU in question this time is a BG one, which are usually alright.
Had no end of trouble with LAP bits in the past, so will not use anymore!
 

Reply to FCU and Led under-counter light problem in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Assuming the electrician checked the new driver was capable of supplying current (in other words it provided an output voltage and curent when...
Replies
1
Views
449
  • Question
Thanks davesparks. Looking at the diagram on the driver that's what I interpreted too, but I heard somewhere that the DALI system doesn't like...
Replies
2
Views
553

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top