Hi all, having a problem on a job...
Using a switched FCU to control some LED under-cabinet strip lights. Customer reported that the lights were staying on after the FCU had been switched off. So I thought the FCU must be stuck in on position, so I replaced the unit.
Had a call from the customer today reporting the same problem.
Upon inspecting the original FCU, it appears to be working as it should. I.e. it isolates both live and neutral.
Any ideas?
Thanks in advance.