Its been along day, I've just finished off with looking around a big garden which has all sorts of electrical things going and would appreciate a bit of advice on VD.

Garden is supplied by 2.5mm SWA (buried), at present taking about 1000W from a 20A MCB in the garage CU. The chap wants 2 greenhouse fan heaters installed. The run is about 40m's in total.

Max allowable VD = 11.5
VD (mV/A/m) for 2.5mm = 18
length = 40m

so available power = (max allowable VD x 1000)/length x VD

= 16A (approx) = 3680W

Garden is already taking 1000W so I'm left with 2680W for 2 greenhouse fan heaters.

I have 2 questions:

1. Can anyone see a half decent greenhouse fan heater that is only 1.3kW?
2. Really, Really tired and just cant figure out if VD means the cable will be unsafe or the MCB more likely to trip.... ridiculous question I know but I've had a glass of port (yeah I'm ready for the jip :rolleyes2:), I'm tired and I just want to figure it out. Quote doesn't even need to be done for a week!
 
stick 'em in, switch on, measure the VD. if it's under 220V at point of utilisation, then start worrying.

You've had a beer! :biggrin:

I'm going to wait for a sensible reply!!!

Route is 30m at present, I will have to add 10m SWA and get it all nicely arranged in both greenhouses. I am not going to 'stick em in'!!! :hand:
 
What is your voltage to begin with? The main concern is that equipment will not work correctly if the voltage drops too low, but I often test premises with upwards of 245v to start with.

Even if it measures 245v should I not be basing it on 230v?
 
Sounds arse about --- to me though, what size heaters does he need for the plants ?

80W or 8000W, once you have sorted that bit rest follows :)

True... I asked him what size, but he hadn't bought them yet. The little bit of research I did this evening showed me that they are usually around 1.5 - 2.8kW!!
 

Reply to Fear of voltage drop! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top