Type 4 devices have trip characteristics of 50×In so you could calculate a maximum Zs value although this is likely to be much less than the manufacturers guidelines, this is because 50× is the worse case scenario due to standards allowing between 10 - 50 × In. It is possible on higher disconnection times the thermal trip is considered over the magnetic trip.
 
Hi does anyone know the type of the Federal “brown” 3871 breakers? The 3 poles have type 4 on them but nothing on the single poles? If they were type 4 the max zs of most circuits wont comply following our EICR.

Many thanks

It’s worth bearing in mind that Federal Electric went under because they fraudulently falsified test results of their MCB’s. There never was a product recall because it was deemed too expensive and it was cheaper to settle any claims through the courts. So it might be prudent to get rid of the fire starters while you have the chance.:)
 
They already don’t meet the maximum earth loop impedance allowed and under the 18th Edition will do so even less. He could also just note the safety implications in the recommendation section of the E.I.C.R. and let the client make up their own mind. It’s all about risk management. I personally have never seen a Federal Electric breaker burned out above 32A. They seem to fair better at higher ratings.
 
It’s worth bearing in mind that Federal Electric went under because they fraudulently falsified test results of their MCB’s. There never was a product recall because it was deemed too expensive and it was cheaper to settle any claims through the courts. So it might be prudent to get rid of the fire starters while you have the chance.:)
If that was true I would have thought they would have been forced to stop selling them and we would have had it all over the trade press.
 
They already don’t meet the maximum earth loop impedance allowed and under the 18th Edition will do so even less. He could also just note the safety implications in the recommendation section of the E.I.C.R. and let the client make up their own mind. It’s all about risk management. I personally have never seen a Federal Electric breaker burned out above 32A. They seem to fair better at higher ratings.
I don't understand they don't meet maximum efli values.
 
My apologies, poor wording on my part. In the opening post the OP stated that most of his circuits were over the max zs threshold on the type 4 breakers. I also don’t know why they are still for sale. Maybe they solved the problem with the breakers but the damage to their reputation was still done.
 

Reply to Federal 3871 “type” required for EICR in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

He only posted the one message then never came back.
Replies
2
Views
844
This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top