I think tbh you need to know exactly what is existing, you cannot design a system by guessing what's existing, like I said earlier, small mistakes cost big in this side of the industry.
 
Yes but you have to look at the bigger picture here, can the fuses be uprated again ie.. is the cable big enough to do so, you want to avoid forcing limitations on future additions, they may just have 100amps because of the low demand but fitted a 200amp system for expansion, we lack the info to give you a true informed reply but your boss really should have done all this and supplied you with the correct gear to start with with which I have my doubt he has.
 
Yes but you have to look at the bigger picture here, can the fuses be uprated again ie.. is the cable big enough to do so, you want to avoid forcing limitations on future additions, they may just have 100amps because of the low demand but fitted a 200amp system for expansion, we lack the info to give you a true informed reply but your boss really should have done all this and supplied you with the correct gear to start with with which I have my doubt he has.
Maybe he couldn't get a 100amp dist-board hence why he got the isolator?but then the cost in price is a huge difference?But he had said to use 25mm tails.il have to run through the design with him tomorrow,thx for the advise really appreciate it.
I only started new job last week so had to make sure I knew what I wax on about before speaking to him.thx
 
Probably be ok but the ratings are based on 90degC remember with tri.
You raise a good point but tri rated still has a higher capacity at 70c plus we do not know the switchgear, the busbar will be ok for 90, I install this stuff all the time and you can maintain the 90c ratings if you choose the correct gear, otherwise it's pointless making it.
 
I'm working in a warehouse and replacing the old fuse boards with a new 3 phase board.
The board will be sitting directly above the buzz bar im not sure if I need to put in an isolator in between them to isolate the 3 phase board?
Thx
Must be a loose connection if the busbar is buzzing:rolleyes:
 

Reply to Feeding 250 amp 3 phase board direct from buzz bar need isolatir in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Sooo the client has accepted that we don't want to be fraudulently taking electricity so that worry is out of the picture. But now basically the...
Replies
32
Views
5K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top