Feeding 250 amp 3 phase board direct from buzz bar need isolatir | Page 5 | on ElectriciansForums

Discuss Feeding 250 amp 3 phase board direct from buzz bar need isolatir in the Commercial Electrical Advice area at ElectriciansForums.net

Yes you need to know the fuse sizes in the switch disconnector for the busbar because if they are 100A this is all unnecessary. If they are 200A then the 125A, 60947-3 switch and the supply conductors need circuit protection, I would guess a 100A 60947-2 main switch at the board would break the bank. Your only option is to use that switch although I am confused by its part no but it looks like the solid links could be replaced with fuses. Shame he opted for that cheap nasty option. You need to go back to square one and confirm the fuses protecting the busbar and remember a 200A switch doesn't necessarily mean 200A fuses.
 
I already answered that Lintay, it depends on the busbar overload protection and that its designed to be 100amp without room for upgrade then yes its totally fine to tail direct to your switch disconnector.

PS the last pic showing the 300amp isolator for the busbar does not tell us what fuses are fitted in it but I suspect they are bigger than 100amps, your boss has thus designed it wrong, picked an isolator instead of a switch fuse and made a pigs ear of it all, get a mccb expansion kit for the board, tail it as required to the size you choose and job done, and tell your boss from me that he really shouldn't be taking on work like this if he doesn't understand the regulations around it, ask him what rating the fuses are in the busbar switch/fuse, if he doesn't know then he hasn't spec'd the job properly.
 
@Lintay

Now we have eventually been given the correct info all but the busbar overload protection size, the info we have provided does explain how this should be done given different circumstances of the busbar fusing size.
There is really nothing more that we can add other than to tell your boss that it's beyond your experience and you need assistance, I would also question where the experienced assistance you need would come from because it sounds like your boss also doesn't understand how to design this kind of job let alone the regulations around it so IMHO he shouldn't be taking on such work, usually for me the hardest part to this work is sourcing busbar clamps to suit the old board as under no circumstance should you double up on existing ones, I also assume you haven't been supplied with heatshrink sleeving for the terminations either all of which is how it should be done professionally.
 
Just a final shot, that supply cable isn't very big not rated at 300A anyway so I suspect you need to look at the source end to confirm. Probably only 63A:eek:
 
Thx guys my boss had agreed to get rid of the isolator and he's ordered a 100 amp mccb kit which he's still adamant 25 mm tails will be ok?
Where the existing boards were that we ripped out we will be using there old points to connect to the bus bar using bolts and washers.shojld I use 8 mm brass bolts?
Thx again
 
Thx guys my boss had agreed to get rid of the isolator and he's ordered a 100 amp mccb kit which he's still adamant 25 mm tails will be ok?
Where the existing boards were that we ripped out we will be using there old points to connect to the bus bar using bolts and washers.shojld I use 8 mm brass bolts?
Thx again

You really need to be asking your boss these questions as oppose to the forum, we are happy to nudge you in the right direction but a step by step guide which your asking for is somewhat abusing our good nature to help, you need to use the appropriate rated busbar clamps that are designed for that busbar system, usually they come in different ratings ie 100amp, 200amp etc, we cannot possible tell you if using the existing is ok as we do not know what has been used and whether they are the official kits or not you want to re-use.
Speak to your boss, if he cannot answer or help you out here, I would politely decline to do the job, he was aware of your experience in the first place, if he drops you on such jobs without the guidance you need or the right kit to do the work then you may want to consider your future options and what you are getting yourself into here, I cannot comment on your circumstances so you may need to just bite the bullet a while and possible look for a company that is willing to support your and train you up in areas you lack experience, mistakes will be made otherwise and sometimes this may put people and property at risk without you realising.
 
This expansion kit will it make the dis board longer tryed asking the wholesalers and they don't know! Thx
You have all the info you require already posted, please help yourself out a little here, I posted a link that shows you the part no's etc of upfront switch gear and expansion kits, if you have any queries ring Scheinder tech' support team, they are very helpful and just explain your inexperience and you have a few questions, and to answer your query, Yes, by the nature of the word 'Expansion' kit, it will indeed make the board longer and needs fitting first before mounting to the framework you intend to fasten to.

You'll need to know the lug hole sizes required to bolt onto the new mccb too while your talking to them, make a list of the part no's you have too so they know exactly what you have.
 
How long have you had the stuttering Finger Westy lol
 

Reply to Feeding 250 amp 3 phase board direct from buzz bar need isolatir in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Sooo the client has accepted that we don't want to be fraudulently taking electricity so that worry is out of the picture. But now basically the...
Replies
32
Views
5K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top