Can you use ferrule crimps on 230v such as power and lighting if you use stranded cables ?
The only thing that comes to mind is what amperage are the rated forCan you use ferrule crimps on 230v such as power and lighting if you use stranded cables ?
I haven't bought them yet was just wondering If it was safe to use them.The only thing that comes to mind is what amperage are the rated for
The only thing that comes to mind is what amperage are the rated for
Not necessarily ferrules can be real small and better chance to heat upYes, also I have never worried about the current carrying capacity of the crimp lug.
A cable is likely to fail beforethe crimp lug.
Ferrules are not the same as crimp lugs in America terminologyNot necessarily ferrules can be real small and better chance to heat up
So the 2.5mm ferrule can only with stand 14A and the 1.5mm 16A so I think you could use them for lighting but not power unless it was LV
So the 2.5mm ferrule can only with stand 14A and the 1.5mm 16A so I think you could use them for lighting but not power unless it was LV
Amazonwhat is your source of this (clearly wrong) information?