Well you could argue, that while for instance a 1.5mm² CPC is acceptable with 2.5mm² circuit conductors, that a 1.5mm² CPC would not be acceptable whith 5mm² circuit conductors.
If run in singles, then the minimum CSA for the CPC would be 2.5mm², which would most likely be sufficient.
That said, it should also be considered, that with all the conductors being in a ring, a break in the CPC would not necessarily be catastophic.
However two breaks in the CPC could well mean that one or more accessory is now no longer earthed.
Whilst that again would not be catastrophic as far as earthing exposed-conductive-parts are concerned (most accessories are plastic), it could be as far as an earth fault ocuuring in whatever item of equipment is connected to the circuit.
As far as lolipop circuits are concerned, no there is no mention in BS7671 of these particular circuits or indeed any othe non-standard circuit.
However, I would still axpect that the requirement to run the CPC as a ring would apply to the ring part of the lolipop circuit.
As for circuits whith high earth leakage.
Whilst all the guides show that it is acceptable to wire using just one CPC, each leg being connected to a separate earth terminal at each accessory.
My understanding of the requirements is that this is incorrect.
The requirements call for two CPCs, running one in the form of a ring does not equal two CPCs, it is still one albeit with two ends.
It is also a requirement that each individual CPC complies with the requirements of Section 543, and that both be suitably sized to act as the individual CPC for the circuit.
One of the Requirements of Section 543, is that the CPC of every RFC be run as a ring.
I really cannot see how running a single CPC as a ring could become two CPCs both run as a ring, simply by using separate earth terminals at each accessory.