I could be wrong but isn't 100ma the minimum recommended assuming it is not required for additional protection.
 
From my research it seems many Sunny Boy inverters are transformerless which means that there is usually no galvanic isolation between the PV dc input and ac output. If you tell me the model number of the inverter I will delve further.

I thought of an experiment you could do which might determine whether the leakage current waveform is ac or dc. At the moment the RCD is type B which can detect the waveforms ac 50Hz, ac 50Hz pulsed, Smooth dc, and ac greater than 50Hz into kHz region - see page 7/21 of:

http://www.doepke.co.uk/download/Techpub-16

The type AC RCD commonly used in Consumer Units can only detect ac 50Hz - it is blind to ac 50Hz pulsed, Smooth dc, and ac greater than 50Hz into kHz region.

What you could try then is inserting a type AC 30mA RCD upstream of the current type B and then observing what happens every morning to the type AC one -does it or does it not trip?

Just an idea for your consideration which might cast a bit more light on the problem by giving information on the waveform of the leakage current (as well as my # 15).
 
Re #24: What you could try then is inserting a type AC 30mA RCD upstream of the current type B and then observing what happens every morning to the type AC one -does it or does it not trip?

I am not suggesting removing the Type B.
 
Answer yourself - I will be interested to read your reasoning.

I have provided a reference which explains why it is right an RCD type B is intalled because there is no dc - ac side galvanic isolation. It may well be the manufacturer of the in-use Sunny Boy inverter says one is not required - one for the OP to clarify - though for me the presence of the type B RCD indicates that the installer has read and abided by the manufacturer's instructions.
 
Answer yourself - I will be interested to read your reasoning.

I have provided a reference which explains why it is right an RCD type B is intalled because there is no dc - ac side galvanic isolation. It may well be the manufacturer of the in-use Sunny Boy inverter says one is not required - one for the OP to clarify - though for me the presence of the type B RCD indicates that the installer has read and abided by the manufacturer's instructions.
The reference you have provided indicates that where required, B type RCDs should be used. i.e. circuits of locations containing baths or showers, socket-outlets or cables concealed in walls.
There is nothing there stating that the supply to or the output from the inverter requires RCD protection.
The OP says that the RCD protects the circuit to the inverter and that the circuit is wired in SWA.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South East
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Fitting a 100ma RCD on Solar PV to solve nuisance tripping.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
53

Advert

Thread statistics

Created
South Spark,
Last reply from
Nigel,
Replies
53
Views
12,255

Advert

TrueNAS JBOD Storage Server

Back
Top