Fitting a 100ma RCD on Solar PV to solve nuisance tripping. | Page 2 | on ElectriciansForums

Discuss Fitting a 100ma RCD on Solar PV to solve nuisance tripping. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

From my research it seems many Sunny Boy inverters are transformerless which means that there is usually no galvanic isolation between the PV dc input and ac output. If you tell me the model number of the inverter I will delve further.

I thought of an experiment you could do which might determine whether the leakage current waveform is ac or dc. At the moment the RCD is type B which can detect the waveforms ac 50Hz, ac 50Hz pulsed, Smooth dc, and ac greater than 50Hz into kHz region - see page 7/21 of:

http://www.doepke.co.uk/download/Techpub-16

The type AC RCD commonly used in Consumer Units can only detect ac 50Hz - it is blind to ac 50Hz pulsed, Smooth dc, and ac greater than 50Hz into kHz region.

What you could try then is inserting a type AC 30mA RCD upstream of the current type B and then observing what happens every morning to the type AC one -does it or does it not trip?

Just an idea for your consideration which might cast a bit more light on the problem by giving information on the waveform of the leakage current (as well as my # 15).
 
Re #24: What you could try then is inserting a type AC 30mA RCD upstream of the current type B and then observing what happens every morning to the type AC one -does it or does it not trip?

I am not suggesting removing the Type B.
 
Answer yourself - I will be interested to read your reasoning.

I have provided a reference which explains why it is right an RCD type B is intalled because there is no dc - ac side galvanic isolation. It may well be the manufacturer of the in-use Sunny Boy inverter says one is not required - one for the OP to clarify - though for me the presence of the type B RCD indicates that the installer has read and abided by the manufacturer's instructions.
 
Answer yourself - I will be interested to read your reasoning.

I have provided a reference which explains why it is right an RCD type B is intalled because there is no dc - ac side galvanic isolation. It may well be the manufacturer of the in-use Sunny Boy inverter says one is not required - one for the OP to clarify - though for me the presence of the type B RCD indicates that the installer has read and abided by the manufacturer's instructions.
The reference you have provided indicates that where required, B type RCDs should be used. i.e. circuits of locations containing baths or showers, socket-outlets or cables concealed in walls.
There is nothing there stating that the supply to or the output from the inverter requires RCD protection.
The OP says that the RCD protects the circuit to the inverter and that the circuit is wired in SWA.
 

Reply to Fitting a 100ma RCD on Solar PV to solve nuisance tripping. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
987
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi all. Try to keep this nice and short. Had an EICR fail on a health centre due to corrosion on main supply which was causing high Ze values...
Replies
0
Views
144
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top