As is stands no main bond at all.. Well not to the origin anyhow. There is a rad on the other side of the DB to which I have been able to attach 10mm bond to and at boiler have connected together all the service pipes to which as the install is all copper then there is continuity..

Its a TNS with ZE @0.43

You gotta be kiddin' me?:earmuffs:


Edit....clarification of the above....:wink_smile:....I think a token effort is possibly worse than no effort at all.As the occupier has managed to survive god knows how many years without main bonding ,unless it's to be done right better to not bother at all!!
 
Last edited by a moderator:
You gotta be kiddin' me?:earmuffs:


Edit....clarification of the above....:wink_smile:....I think a token effort is possibly worse than no effort at all.As the occupier has managed to survive god knows how many years without main bonding ,unless it's to be done right better to not bother at all!!

I fail to see what you mean.. Yes of fair enough it not right and there is no way id charge a customer for the same work however..

A) Its by far safter than before
b) Allthough bonding not in correct places still connected to MET..

Please explain bud?
 
Not having a go mate....just if another spark comes in at a later date and sees the only main bond on a rad? I see where you are coming from though.

Same principle applies to additional sockets,I confess to having installed extra sockets in old ladies bedrooms without RCD/bonding. Because it's been like that for decades without a problem and one extra socket not likely to supply anything outside changes nothing ....and few old ladies want to spend forty quid on a socket and then another 300 providing RCD's and bonding....and I flatly refuse to subscribe to the lunacy of an RCD FCU for one socket/buried cable in a bedroom when nothing else in the entire property is RCD'd!
 
This thread will probably cause outrage but here goes.. Changes a DB a year ago from my 89 year old gran, She is proud of here house and spent a load on it recently doing it up..

Well I say loads... The electrics aint been touched in aged and well to be fair needed a test..

Giving she lives a while away I am ashamed I dont visit very often.. Well she called as her lights had fused after trying to poke around in the fuseboard trying to change a 3036 she gave in and called an emergency electrician who charged her £120 for out of hours call out but did not refuse as they say that the house needed a rewire..

So i take the time off go up and see her, IR test and then ZE, rejuice and ZS however the board if on its last legs and seen better days.. After a chat I agree to fit a new RCD board but she is stuborn about running cables to install bonds due to having to lift freshly laid wooden flooring.. She would rather leave whats there there instead of lifting flooring..

So i crack on fit board...

Call me whatever you want but I know for a fact at 89 year old the system is by far safer to my gran now then it was..

Would I do it again.. Depends on the circumstances.............
I understand where you are coming from, you know, and so do we all that have elderly relatives the upset that major work can cause. you did what you could to make it safe within the perimeters that your Gran could in your opinion cope or agree with. Although I could not possibly agree publicly, I do understand. Now you just need to make a point of visiting on a regular basis and upgrade as and when the opportunity arises. Good luck on that one mate.
 
I understand where you are coming from, you know, and so do we all that have elderly relatives the upset that major work can cause. you did what you could to make it safe within the perimeters that your Gran could in your opinion cope or agree with. Although I could not possibly agree publicly, I do understand. Now you just need to make a point of visiting on a regular basis and upgrade as and when the opportunity arises. Good luck on that one mate.

"b) Allthough bonding not in correct places still connected to MET.."

Yeah mate until plumber gets in or DIY neighbour then that 'bond' on the rad means diddly squat with plastic fittings and pipes all over the place.

Main bonding goes where it should......... on extraneous conductive parts........gas/water/oil etc not on a flippin radiator fgs.......no short cuts whether its for granny/auntie or not IMO.
But hey........if your comfortable with it being safer than it was then good.
 
As is stands no main bond at all.. Well not to the origin anyhow. There is a rad on the other side of the DB to which I have been able to attach 10mm bond to and at boiler have connected together all the service pipes to which as the install is all copper then there is continuity..

Its a TNS with ZE @0.43

If it's TNS with a Ze of <0.5, there's a solid 10mm bond from the MET to the pipework at the radiator, all the plumbing is copper plus there's crossbonding at the boiler and you've upgraded to RCD (and I assume you've tested all circuits with the CU change) then I wouldn't be too worried. Sounds to me like the installation is far safer than you found it.
 
And I got shouted at when I proved bonding to the nearest point on a gas pipe would give a better reading than fighting to get a to the meter.

Given the wall thickness of BS copper pipe to be 0.8mm 15 / 22mm provide a far better conductive path than even 16mm cable.

Where:
Od = outer diameter
Id = inner diameter

π*(Od/2)²-π*(Id/2)²=CSA/mm²
15mm ≡ 39.69mm² 248.06% ↑
22mm ≡ 53.28mm² 362.75% ↑

% improvement based on 16mm²
 
i'm totally with you there, tony. our gas is bonded on the gas pipe where it passes within 6" of the CU. sod drilling a 11" cavity wall into the garage just to run an extra 20ft. to the point of entry.
 
i'm totally with you there, tony. our gas is bonded on the gas pipe where it passes within 6" of the CU. sod drilling a 11" cavity wall into the garage just to run an extra 20ft. to the point of entry.


Especially as it is a continuas copper pipe but you have raised the old BG chestnut where they make their money on as O Dear your gas pipe is not earthed properly as the earth bond is not at the meter
 

Reply to Fitting a DB without updating the main bonding.. Bad crack or safer than before? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top