Hi, I’m after a bit of advice please, my ceramic hob has cracked so I’ve bought a new one with the intention of fitting it myself. The new hob has now arrived but it’s got a cable already fitted which has 4 wires, L1, L2, N and E.

The cable fitted to my old hob has only three wires, is it possible to fit the existing 3 wire cable to the new hob? The diagram inside the book for the new hob also shows three wires.

I have added some pictures, the first three are the existing hob and the rest are the new hob and booklet.

I’ve previously replaced plug sockets and light fittings myself, but if it’s a case of wiring the new hob into the wall then I’ll be leaving that to an electrician.

any help would be appreciated,

thanks
 

Attachments

  • [ElectriciansForums.net] Fitting new ceramic hob
    82C36209-6766-4843-9D5A-5F23B981309F.jpeg
    115.6 KB · Views: 49
  • [ElectriciansForums.net] Fitting new ceramic hob
    45802B6F-4CB9-43B4-8EEC-0FA210532186.jpeg
    74.6 KB · Views: 52
  • [ElectriciansForums.net] Fitting new ceramic hob
    96B2102E-4100-4830-A7E9-7D6F430F28C9.jpeg
    71.5 KB · Views: 55
  • [ElectriciansForums.net] Fitting new ceramic hob
    910FCD9F-BB3D-435B-84AB-77D47CBC0DC5.jpeg
    124.2 KB · Views: 61
  • [ElectriciansForums.net] Fitting new ceramic hob
    80A8F6F7-6A80-4871-8F54-F02638609B9F.jpeg
    78.8 KB · Views: 61
  • [ElectriciansForums.net] Fitting new ceramic hob
    FD5974AD-E130-460B-A78D-ABC4F27627AE.jpeg
    81.2 KB · Views: 57
  • [ElectriciansForums.net] Fitting new ceramic hob
    E9F5BE94-EEA3-40B2-A8FD-D228268B11D6.jpeg
    134.3 KB · Views: 53
Welcome to the forum mate.

We were just talking about this at work today.
One of the guys sons has just bought a hob that has 4 wires.

L1 & L2 wire to the L
N wires to N
E wires to E
 
In some EU countries the maximum size of mcb allowed in domestic installations is 16A. so hobs and cookers are split across two linked mcb's. Usually both on the same phase but can be across two phases.
In my opinion this is much better than the UK way of sticking all the rings onto one 32A mcb.
So as above, link L1 and L2.
 
I have a question?

All the cables are the same size.
The Live cables are basically in parallel, shouldn't the Neutral cable be equal size to the two Live cables in parallel? Or am I having a brain fart moment...
 
Some of the hobs I've fitted, provided links for the hobs terminals when connecting as single phase.

Do are EU member countries have 3 phase domestic supplies? Not that will matter anytime soon.
 
I have a question?

All the cables are the same size.
The Live cables are basically in parallel, shouldn't the Neutral cable be equal size to the two Live cables in parallel? Or am I having a brain fart moment...

I thought that, however if the N is able to take the 25A the manufacturer says it can draw then all is fine.
in theory you could reduce the size of the live conductors to 1.5mm as each can only draw 12.5A but the N will have to take the full 25A if on a single phase. I think for simplicity they have just over sized the cable.
 
I thought that, however if the N is able to take the 25A the manufacturer says it can draw then all is fine.
in theory you could reduce the size of the live conductors to 1.5mm as each can only draw 12.5A but the N will have to take the full 25A if on a single phase. I think for simplicity they have just over sized the cable.

Looks like the cable is 4mm csa conductors ?
 
looking at that diagram for 2nd time, it would appear that both L1 and L2 should be connected to L, for use on 240V single phase. see also post #4. so it appears that both black and brown should be commoned to L supply.
 

Reply to Fitting new ceramic hob in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Great! Thanks so much for your help. I’ll have a dig around that site and others and see what I can find :) Cheers
Replies
2
Views
187
"It works" and "it's safe" are not necessarily the same thing. With DIY work, they are often far from the same thing.
Replies
7
Views
729

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top