Fitting new CU to TT system and old BS fuse box | on ElectriciansForums
Discuss Fitting new CU to TT system and old BS fuse box in the UK Electrical Forum area at ElectriciansForums.net
Essex
Hi there, new to this site and just after a bit of advice. I am part qualified as a Domestic Electrical Installer and am just waiting for the course to complete my Part P.
I have been asked to install a new Consumer Unit on a TT system in a very old cottage. As seen in the photographs, the current system is the old BS, but I am a little concerned that on examination, the CPS appears to be only 2.5mm where I would have thought it should be 10mm minimum.
Any advice would be greatly received.
Chris
[ElectriciansForums.net] Fitting new CU to TT system and old BS fuse box
Welcome to the forum chris, if your still on a training course you might be interested in applying for our Trainee section where we have selected mentors to help with the level of question a trainee asks.
Regarding the pic ...are they exposed live terminals as you found them?????
Many thanks for the advice. I took the covers off the terminals so they are not normally exposed like that.
Regards,
Chris
Chris
Why would it need a 10mm2?
Agreed .... Possibly the most immediately important question that the OP throws up ...this needs answering first before any of the many other questions regarding this potential work !!!
Thanks a lot. I'll upgrade it to 10mm. Thanks guys
Why 10mm?
First get the DNO out to see if an earth connection can be made, it usually can these days.
If not then you'll need to install new earth electrodes (the little twig that goes with the voelcb is unlikely to be any good) to achieve a stable and low Ra.
Calculate the required size of protective conductor using the adiabatic equation, assess the required size of main bonding and then select a suitable earthing conductor.
When doing my Ra, test my understanding is that I need to do it from the mccb / RCD and the incoming earth bar connection. The definition of Ra is given as - the sum of the resistances of the earth electrode and the protective conductor(s). I know we don't use the Zs reading although I have been told it the same. My understanding is that RA is the sum of the resistances of the earth electrode and CPC multiplied by the RCD operating current. This needs to be 50V or less. As you can tell, I'm very much in the early stages and appreciate all the advice and guidance.
Many thanks.
Reply to Fitting new CU to TT system and old BS fuse box in the UK Electrical Forum area at ElectriciansForums.net