Fitting new CU to TT system and old BS fuse box | on ElectriciansForums

Discuss Fitting new CU to TT system and old BS fuse box in the UK Electrical Forum area at ElectriciansForums.net

Joined
Sep 28, 2015
Messages
13
Reaction score
0
Location
Essex
Hi there, new to this site and just after a bit of advice. I am part qualified as a Domestic Electrical Installer and am just waiting for the course to complete my Part P.

I have been asked to install a new Consumer Unit on a TT system in a very old cottage. As seen in the photographs, the current system is the old BS, but I am a little concerned that on examination, the CPS appears to be only 2.5mm where I would have thought it should be 10mm minimum.

Any advice would be greatly received.

Chris

[ElectriciansForums.net] Fitting new CU to TT system and old BS fuse box






[ElectriciansForums.net] Fitting new CU to TT system and old BS fuse box
 
Welcome to the forum chris, if your still on a training course you might be interested in applying for our Trainee section where we have selected mentors to help with the level of question a trainee asks.

Regarding the pic ...are they exposed live terminals as you found them?????
 
Welcome to the forum chris, if your still on a training course you might be interested in applying for our Trainee section where we have selected mentors to help with the level of question a trainee asks.

Regarding the pic ...are they exposed live terminals as you found them?????


Many thanks for the advice. I took the covers off the terminals so they are not normally exposed like that.

Regards,

Chris
 
Hi there, new to this site and just after a bit of advice. I am part qualified as a Domestic Electrical Installer and am just waiting for the course to complete my Part P.

I have been asked to install a new Consumer Unit on a TT system in a very old cottage. As seen in the photographs, the current system is the old BS, but I am a little concerned that on examination, the CPS appears to be only 2.5mm where I would have thought it should be 10mm minimum.

Any advice would be greatly received.

Chris

[ElectriciansForums.net] Fitting new CU to TT system and old BS fuse box






[ElectriciansForums.net] Fitting new CU to TT system and old BS fuse box

Why would it need a 10mm2?
 
Welcome to the forum chris, if your still on a training course you might be interested in applying for our Trainee section where we have selected mentors to help with the level of question a trainee asks.

Regarding the pic ...are they exposed live terminals as you found them?????

Agreed .... Possibly the most immediately important question that the OP throws up ...this needs answering first before any of the many other questions regarding this potential work !!!
 
Thanks a lot. I'll upgrade it to 10mm. Thanks guys

Why 10mm?

First get the DNO out to see if an earth connection can be made, it usually can these days.
If not then you'll need to install new earth electrodes (the little twig that goes with the voelcb is unlikely to be any good) to achieve a stable and low Ra.
Calculate the required size of protective conductor using the adiabatic equation, assess the required size of main bonding and then select a suitable earthing conductor.
 
When doing my Ra, test my understanding is that I need to do it from the mccb / RCD and the incoming earth bar connection. The definition of Ra is given as - the sum of the resistances of the earth electrode and the protective conductor(s). I know we don't use the Zs reading although I have been told it the same. My understanding is that RA is the sum of the resistances of the earth electrode and CPC multiplied by the RCD operating current. This needs to be 50V or less. As you can tell, I'm very much in the early stages and appreciate all the advice and guidance.
Many thanks.
 
No, Ra for an installation is the combined the resistance to earth of all connected earth electrodes.
Ra is also used with reference to a single electrode.

Testing can be carried out in a number of ways, which generally require an earth resistance tester of some type. The most common method being the 3 wire fall of potential method.
It is possible to obtain an approximation of Ra through use of an earth loop impedance tester where the measured Ze minus half the measured L-N loop impedance is used.
 
...It is possible to obtain an approximation of Ra through use of an earth loop impedance tester where the measured Ze minus half the measured L-N loop impedance is used.

And since it's the Ze (& Zs) that really matters with regard to earth fault disconnection times, if you have a supply already on site it's not a bad way of doing it (unless you really need to know an accurate figure for Ra).
 
YOU are a star! I really appreciate all of this expertise and advice. As you can tell, as much as I am fairly confident in my abilities, there is an awful lot to learn and experience is the greatest of them all. Thank you for all your help.

Kind regards,

Chris
 
And since it's the Ze (& Zs) that really matters with regard to earth fault disconnection times, if you have a supply already on site it's not a bad way of doing it (unless you really need to know an accurate figure for Ra).

I guess it depends on whether you are happy with an approximation which can be affected by external influences or if you prefer to measure it properly.
 
YOU are a star! I really appreciate all of this expertise and advice. As you can tell, as much as I am fairly confident in my abilities, there is an awful lot to learn and experience is the greatest of them all. Thank you for all your help.

Kind regards,

Chris

Yes it is clear you need a lot more experience. You are obviously not ready to be working away from your mentor yet. How far through your apprenticeship are you?
 
Final stages of course and then a weeks practical for the Part P, but it's experience I lack. I have studied in my own time whilst employed elsewhere and not in the electrical industry. Scary times but I intend to take this very slowly and seek help and advice at all times.
 
Final stages of course and then a weeks practical for the Part P, but it's experience I lack. I have studied in my own time whilst employed elsewhere and not in the electrical industry. Scary times but I intend to take this very slowly and seek help and advice at all times.

So you are setting up in business as an electrician with no practical experience ?
 
Final stages of course and then a weeks practical for the Part P, but it's experience I lack. I have studied in my own time whilst employed elsewhere and not in the electrical industry. Scary times but I intend to take this very slowly and seek help and advice at all times.


Can you please explain what this entails?
 
Final stages of course and then a weeks practical for the Part P, but it's experience I lack. I have studied in my own time whilst employed elsewhere and not in the electrical industry. Scary times but I intend to take this very slowly and seek help and advice at all times.

Thats called an apprenticeship!!!
 

Reply to Fitting new CU to TT system and old BS fuse box in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Absolutely, yes. It was just a bit of a joke, looking at your quoted Z values. edit. Oh, joking too!.....I see your attempted smile didn't work ...
2
Replies
28
Views
6K
i would split he tails and fit an additional 2/3 way CU to supply the garage/whatever. that way you could feed in SWA, installung RCDs as and if...
Replies
3
Views
4K
  • Question
Really, what awful news. I feel terrible. He was incredibly helpful. Thank you for letting me know. 👍🏻
2
Replies
47
Views
6K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
489
  • Question
As above, it is the number of live cores (i.e. current-carrying) as they are the contributors to the cable heating. So in single-phase you have 2...
Replies
9
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks