Alright I'll be a brave boy bloody awful rip it out and start again, complete crap
 
Hi,

I don't know where to start , there is so much wrong with it. As Pete says rip it out, start again and do it right. Trying to put right what is already there will take longer than re-doing the job.

Regards.
 
Trunking already in situ, M/C Switch fuses bushed into said trunking underneath, SWA terminated into said trunking, unsheathed SWA core run into individual Switch fuses with appropriate earth sleeveing . Insulated and sheathed tails run to DNOs equipment, all nice and neat and safe oodles of space left
 
y4ebype4.jpg
 
I think you've already stated your doing one but before I'd even consider touching this stuff it would be a day or two of indepth inspection/test (EICR) to baseline the whole installation --- if you think it looks bad at this end I be scared sh*tless would might have happened at the flat ends!. Then and only then can you discuss the way fwd with whoever owns the place and how you are going to rectify & certify it?!?!
 

Reply to flat submains and landlords suuply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
768
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

I challenged a council on having the same system installed in an HMO. One consideration is if the flats/escape route were made to The Building...
Replies
1
Views
437
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
485

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top