S30/31 is no demand from Heating side, as you probably already know.
When the Boilers arrive from new they are linked out on 24V side normally so they will work without any controls by using the user interface.
If the mode button is not working at all and the harness from the user interface is good, then it sounds like the interface is faulty.
I haven't seen this of course and as you know, it's difficult to diagnose faults on the forum sometimes. It's a bit like discussing things with someone over the phone.
 
I don't know. When I joined here It just accepted my user name from over there. @Corbs will probably know tbh.

Are there no fault codes?
Have you tried linking L-R since you took the pressure down?

nope last different accounts there not connected so, requires registration / create an account
 
S30/31 is no demand from Heating side, as you probably already know.
When the Boilers arrive from new they are linked out on 24V side normally so they will work without any controls by using the user interface.
If the mode button is not working at all and the harness from the user interface is good, then it sounds like the interface is faulty.
I haven't seen this of course and as you know, it's difficult to diagnose faults on the forum sometimes. It's a bit like discussing things with someone over the phone.

I totally understand what your saying. If you were there on site, You'd have most likely figured this out in a very short space of time. I've had a chat with a few other people at work and they reckon it could be down to the interface as well. Some were left scratching their heads in wonder why you can't control the C/H setpoint from the display itself with the removal of an external demand.

I really do wish this boiler was different or at the very least, bloody well working. I'm hearing some proper horror stories about the Glow Worm 24/30cx's.

Not good at all.
 

Reply to Flexicom 30cx - H/W but no C/H in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

The 4 pumps are :- 1. boiler to cylinder 2. C/H and UFH circulating pump 3. UFH dedicated pump after manifold 4. DHW circulating pump. (this just...
Replies
4
Views
2K
  • Question
You need a wi fi switch that is compatible with your switchbot thermostats. Remove the SCR, use the neutral and live to power the wifi switch, and...
Replies
8
Views
958

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top