Hi guys, for those of you into testing a lot, using a Fluke 1652C all in one tester. What does EER 5 mean when testing? I'm told it could mean noise. Could someone explain please?
The test are mainly carried out on larger size distribution cables (longer runs etc) as opposed to domestic installations. Would you say that the flukes are aimed at the domestic market? Thanks
 
Error 5 does indeed indicate noise, however a work around (provided the circuit isn't rcd protected) is to select the L-N option.
Null the leads, then connect the L to phase and N to earth.
This will give you a fast Zs reading that's proven very accurate on a properly calibrated fluke when comparing those readings with other makes of tester.
 
Error 5 does indeed indicate noise, however a work around (provided the circuit isn't rcd protected) is to select the L-N option.
Null the leads, then connect the L to phase and N to earth.
This will give you a fast Zs reading that's proven very accurate on a properly calibrated fluke when comparing those readings with other makes of tester.

The anti trip low current test should not be used for non RCD circuits, the high current test should always be used as the first option.
 
The anti trip low current test should not be used for non RCD circuits, the high current test should always be used as the first option.

Agreed Dave,
My post relates to those models in the flook range that don't have the high current option ie the 1651 without b or c prefix.
With those models, if you connect the way I describe, your effectively performing a high current test.
Of course high current is not an option with rcd's in circuit for obvious reasons.

To the OP your Flook 1652C DOES have high current option.
 
Last edited by a moderator:
Agreed Dave,
My post relates to those models in the flook range that don't have the high current option ie the 1651 without b or c prefix.
With those models, if you connect the way I describe, your effectively performing a high current test.
Of course high current is not an option with rcd's in circuit for obvious reasons.

To the OP your Flook 1652C DOES have high current option.

Then those testers are not fit for purpose!

High current testing is possible with RCDs in the circuit using the alternative Zs test method. The only time it's not really possible is with ring circuits.
 

Reply to Fluke tester in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Sticky
  • Question
Best Electrical Courses I endeavour to create a "best electrical courses" thread for 2025 (so training courses that did well during 2024 are the...
Replies
0
Views
1K
I wouldn't rely on the ghost immobiliser on its own. My hire vans had them fitted, we lost a key and had a guy come out to cut and programme a new...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top