Hi there went a job today to supply a light box for a shop today, it has 30 fluorescent tubes inside it done the cable calc 30 x 58watts = 1740
1740/240=7.25
So I fitted a 10amp rype b mcb and it tripped so I clamped the load going out it was reading 10.8amps and on start up it was hitting 11-12 Amps.
Now I'm thinking of fitting a 10amp type c mcb will this do it
Has anyone come across this??
1740/240=7.25
So I fitted a 10amp rype b mcb and it tripped so I clamped the load going out it was reading 10.8amps and on start up it was hitting 11-12 Amps.
Now I'm thinking of fitting a 10amp type c mcb will this do it
Has anyone come across this??