This is on the ESC website.
I would love to see what other code 1 observations were made if he classes this as Danger present Risk of injury.
So what did he do to elimanate that risk????????
SOCKET-OUTLET(S) | S | S181-5 | Earthing of enclosure (back box) | | |
Contents
1. Introduction
2. Where the cpc is a single-core cable or a core of a cable, connected directly into the earthing terminal of a socket-outlet
2.1 Metallic box with two fixed (non-adjustable) lugs
2.2 Metallic box with two adjustable lugs
2.3 Metallic box with one fixed and one adjustable lug
3. Where the cpc is formed by metallic conduit, trunking or ducting, or the metal sheath or armour of a cable
1. Introduction
Guidance is provided in this topic on whether it is necessary to install a so-called ‘earthing tail’ between a socket-outlet and an associated metallic back box. The guidance applies where protection against electric shock is by automatic disconnection of supply, as it is in the vast majority of cases.
A metallic back box for a surface-mounted socket-outlet is an exposed-conductive-part, and a metallic back box for a flush-mounted socket-outlet is deemed to be an exposed-conductive-part (even though it may not be able to be touched). Therefore, such back boxes, no less than every other exposed-conductive-part, are required to be earthed in accordance with Regulations 411.4.2 (TN systems) and 411.5.1 (TT systems) of BS 7671.
However, depending upon certain characteristics of the circuit protective conductor (cpc), the socket-outlet and its box, an ‘earthing tail’ may or may not be required between the socket-outlet and back box.
2. Where the cpc is a single-core cable or a core of a cable, connected directly into the earthing terminal of a socket-outlet
An earthing tail may not be required where the cpc associated with the circuit wiring from a distribution board to a socket-outlet takes the form of a single-core cable or a core of a cable, and is connected directly to the earthing terminal of the socket-outlet.
Whether an earthing tail is required depends upon whether one or both of the lugs on the back box are adjustable (to permit the socket-outlet to be levelled), and upon the earthing strap and eyelet arrangement of the socket-outlet, as detailed in items 2.1, 2.2 and 2.3.
| |
| |
| 2.1 Metallic box with two fixed (non-adjustable) lugs
The provision of an earthing tail is not required between a socket-outlet having an earthing strap and either one or two eyelets, and metallic back box as shown in Fig 1 (although the fitting of an earthing tail is still desirable). The box can be considered adequately earthed through the earthing straps and eyelets of the socket-outlet and the fixing lugs on the box.
2.2 Metallic box with two adjustable lugs
An earthing tail must be fitted between a socket-outlet and a back box having two adjustable lugs, such as the box shown in Fig 2. The need for this has been demonstrated where socket-outlets have suffered overheating and burning around the fixing holes due to a line-to-earth fault in metal boxes which had not been provided with an earthing tail. Because the adjustable lugs had become corroded, they presented a high resistance to the earth fault current, and consequently the circuit overcurrent protective device did not operate within the maximum time permitted by BS 7671. This resulted in a risk of electric shock as well as the thermal effects already mentioned.
Fig 1
|
| |
| Fig 2
2.3 Metallic box with one fixed and one adjustable lug
Care must be exercised when installing back boxes having one fixed lug and one adjustable lug, as shown in Fig 3, because some socket-outlets have only one earthing strap and eyelet. It must be ensured that the earthing eyelet is located at the fixed lug position, otherwise an earthing tail must be provided.
Photograph courtesy of Legrand Electric Ltd.
Fig 3
3. Where the cpc is formed by metallic conduit, trunking or ducting, or the metal sheath or armour of a cable
Regulation 543.2.7 of BS 7671 requires an earthing tail to be fitted where the cpc associated with the circuit wiring from the distribution board to the socket-outlet is formed by metallic conduit, trunking or ducting, or the metal sheath or armour of a cable. The earthing tail must connect the earthing terminal of the socket-outlet to the earthing terminal incorporated in the associated back box (see Fig 4).
|
| |
| An ‘earthing tail’ is required where the protective conductor is formed by metallic conduit, trunking or ducting, or the metal sheath and/or armour of a cable
Fig 4
The purpose of the earthing tail is not to earth the back box but to earth the socket-outlet (by connecting it to the back box).
The earthing of the back box itself is reliant upon the metallic conduit, trunking, ducting, or metal sheath or armour of a cable, forming the cpc. The requirements of BS 7671 relating to the use of such parts of a wiring system as a cpc are discussed in Topic P157-7.
|