very interesting, a regulation that condones skimping, can anyone tell me what is achieved by not fitting a fly lead, apart from the saving of 100mm of copper and a bit of sleeving. I am really glad that I am not working day to day in domestic any more!

I regularly nowadays come across back-boxes with one adjustable lug with no provision for a fly and they are passed to BS so I guess that says it all. Personally I fit them as a matter of course but Ive heard arguments saying you are more likely to create a problem by having 3 x cpc going into the earth on the back of a socket as its more likely to pull out than having 2. No way its a 1 on a PIR though, thats bonkers
 
The above qouted is actually(or appears to be) guidelines, not regulations. The guidelines say that in certain circumstances, the tail can be omitted, and goes on to list those circumstances. Unfortunately it is very flawed. this statement:

"The guidance applies where protection against electric shock is by automatic disconnection of supply, as it is in the vast majority of cases"

made me laugh out loud, as RCD protection is by no means universal. It may exist in the "vast majority" of new buildings. but in the rest it is simply not there! The "vast majority" of the domestic and commercial properties I enter are over 15 years old, and generally still use rewirable fuse protection.

Basically what it says is you can omit a flylead if one of the socket front fixing lugs is fixed, or the box is earthed by SWA or metal conduit and a seperate earth or cpc is connected to the socket front, BUT ONLY IF THE WHOLE IS RCD PROTECTED!!
However, take the situation where some scumbag hasn't used a grommet in a metal box and the insulation is damaged. When sparky looking for a fault comes along and removes the socket front ,fault clears because the only earth on the box is via the screw, but the box remains live when he restores power to give the sparky a belt when he comes back to it! As I have said in my earlier post ommiting flyleads is just skimping. As professionals , and I am now speaking to the time served properly qualified amongst us, we are supposed to use the IEE regs plus our common sense and experience to produce an installation that is safe in all circumstances. If you need a regulation to back up everything you do,and look for regulations that justify doing less than what will be safe in every circumstance, you are not fit to call yourself an electrician
 
very interesting, a regulation that condones skimping, can anyone tell me what is achieved by not fitting a fly lead, apart from the saving of 100mm of copper and a bit of sleeving. I am really glad that I am not working day to day in domestic any more!
Personally I don't do it, never have, if BS7671 reckons it's safe, I'll go with that.

The fact is, as long as the faceplate is fitted correctly, the backbox is going to be earthed by the screws, if the plate is off, then the installation is not in a safe completed state anyway and anyone unscrewing a live faceplate should realise this and realise that if the live wire jumps out (which it won't) and lands on the now unearthed backbox, said box will give them a belt. If they don't realise this and they get a belt, well, they'll know for next time.

Fact is I do good work, I use gromets, do my screws up properly, always have RCD protection (in houses) etc one of my backboxes isn't just going to magically become live and kill someone.

For me, time is money, I work for myself I'm always busy, rarely get away from a job before 5pm and anything that can save me time without breaking rules or affecting finished quality, I embrace.
 
Last edited by a moderator:
Fair enough Dave 85, but if you re read my post you will see that I describe the conditions where the back box will be live, and it does not involve any wires jumping out. Some ppl will put up with a lowering of safety standards, some will not. I rarely if ever go back to my own work, it is usually the work of others that causes problems, and that is also the place where accidents happen to unwary sparks!
 
Incidentally, Dave 85 if you NEVER do it, you are probably breaking guidlines in certain circumstances. BS7671 does not say you never need to fit a fly lead, it tells you under which circumstances you may omit a flylead. If the box has no flylead terminal, perhaps you are buying the wrong boxes for the circumstances, and perhaps this lowering of safety standards has been brought about by manufacturer lobbying in order to make box manufacture cheaper:)
 
Unfortunately it is very flawed. this statement:

"The guidance applies where protection against electric shock is by automatic disconnection of supply, as it is in the vast majority of cases"

made me laugh out loud, as RCD protection is by no means universal. It may exist in the "vast majority" of new buildings. but in the rest it is simply not there! The "vast majority" of the domestic and commercial properties I enter are over 15 years old, and generally still use rewirable fuse protection.

Basically what it says is you can omit a flylead if one of the socket front fixing lugs is fixed, or the box is earthed by SWA or metal conduit and a seperate earth or cpc is connected to the socket front, BUT ONLY IF THE WHOLE IS RCD PROTECTED!!

Are you saying that protection by "automatic disconnection of supply" requires an RCD?

Not true. ADS is the normal means of protection using rewirable fuses, MCBs, etc. See BGB 411.
 
please quote the relevant passage of BGB 411 whatever that is, as I can find no online reference to it. A rewirable fuse is certainly NOT ADS as far as I am concerned, and if you read my above post, you would see that in the circunstances suggested a rewirable fuse would allow lethal current flow to occur. You are arguing a defenceless point because safety is reduced if the fly lead is omitted, and enhanced if it is fitted. Common sense says it should be there, the problem today is that too many regulations are unclear and conflicting, and common sense is anything but common. I would suggest if your profit margin depends on saving 30 minutes on an entire install by not fitting fly leads, you have misquoted for the job.
 
"BGB" is BS 7671:2008 Incorporating Amendment No.1: 2011, Requirements for Electrical Installations. Section 411, "Protective Measure: Automatic Disconnection of Supply".

You do have a copy, don't you?
 
No, I don't, and never have had, I work to the IEE regs and ammendments, and as you will understand if you have read my above posts, I am not involved in day to day installation any more, so I have no need of one. Neither do I use regulations as an excuse for not thinking. What I do have is a five year apprenticeship at a NICEIC approved contractor from 1967 to 1972, a City and Guilds National diploma in electrical engineering (three years at tech college) and 40 years experience and the certain knowledge that if I had omitted fly leads in socket boxes I would not only have failed my first year at college, I would also have got my backside royally kicked at work. As I have said above, some people will put up with falling standards, some will not. If you have the relevant documentation, please quote from it. I have detailed above the circumstances in which the lack of a fly lead would make an instalation dangerous to an electrician investigating a fault, I stand by it.
 
The above qouted is actually(or appears to be) guidelines, not regulations. The guidelines say that in certain circumstances, the tail can be omitted, and goes on to list those circumstances. Unfortunately it is very flawed. this statement:

"The guidance applies where protection against electric shock is by automatic disconnection of supply, as it is in the vast majority of cases"

made me laugh out loud, as RCD protection is by no means universal. It may exist in the "vast majority" of new buildings. but in the rest it is simply not there! The "vast majority" of the domestic and commercial properties I enter are over 15 years old, and generally still use rewirable fuse protection.

Basically what it says is you can omit a flylead if one of the socket front fixing lugs is fixed, or the box is earthed by SWA or metal conduit and a seperate earth or cpc is connected to the socket front, BUT ONLY IF THE WHOLE IS RCD PROTECTED!!
However, take the situation where some scumbag hasn't used a grommet in a metal box and the insulation is damaged. When sparky looking for a fault comes along and removes the socket front ,fault clears because the only earth on the box is via the screw, but the box remains live when he restores power to give the sparky a belt when he comes back to it! As I have said in my earlier post ommiting flyleads is just skimping. As professionals , and I am now speaking to the time served properly qualified amongst us, we are supposed to use the IEE regs plus our common sense and experience to produce an installation that is safe in all circumstances. If you need a regulation to back up everything you do,and look for regulations that justify doing less than what will be safe in every circumstance, you are not fit to call yourself an electrician

I have had that exact fault many times, haven't really got time for sloppiness.
Always grommets and tagged boxes, where no fixed lugs.
Most metal boxes I've come across recently don't even have earth terminals......
And as said previously they have the same bs number......
 
No, I don't, and never have had, I work to the IEE regs and ammendments, and as you will understand if you have read my above posts, I am not involved in day to day installation any more, so I have no need of one.

Sorry, I hadn't realised that you've been out of the game for a while.

The IEE Wiring Regs became BS7671 at the sixteenth edition. In that edition, the section I refer to is 413-02 "Protection by earthed equipotential bonding and automatic disconnection of supply", and in the fifteenth edition it's 413-2.
 
Fine, mate, no problem, but I still can't see that a rewirable provides Automatic dissconection, I would want a circuit breaker for that, especially if it was me providing the live to earth path at the other end. As I have said, it is our responsibility according to the (old) IEE regulations to provide an installation that is a safe as it can be in all forseeable circumstances. I personally have never seen socket boxes without earth/cpc/connections, but in this day and age nothing really surprises me.Standards have been alowed to fall dramatically. Don't even get me started on part P!
 
Fine, mate, no problem, but I still can't see that a rewirable provides Automatic dissconection, I would want a circuit breaker for that,

the whole meaning of ADS is nothing to do with RCDs. it's disconnection of supply in the event of a fault. the impedance of the fault path dictates the time taken for the OCPD to operate, whether it be a MCB or a fuse. no OCPD will operate at the sort of level of current that will kill you, that's why we have RCDs AS ADDITIONAL PROTECTION. i do agree with you that fitting flyleads is good practice.
 
"no OCPD will operate at the sort of level of current that will kill you, that's why we have RCDs AS ADDITIONAL PROTECTION"

Which is exactly what I have said! if there is no RCD, and in my experience installations over twenty years old, and there are millions out there, have no RCD, and will kill you if you become the fault path between an unearthed box that has become live due to insulation damage, and an earthed socket front, if the circuit is only protected by rewirables.
 

Reply to Flying leads and the regulations. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
679
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
698

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top