A small under counter AEG fridge. Instructions say it is fitted with a 13A fuse in the plug. Also states it must be replaced by a 13A fuse. The fridge is drawing 0.32 amps. A 13A fuse is ridiculously oversized. If having a mcb or RCBO at the CU for just the fridge, a 1.00mm cable can be run on a radial for it.

The instructions do say that a qualified or competent electrician must fit the appliance, so a get out for them. If the electrician say 3A will do then that is that I suppose. Do many ignore these types of instructions and say insert a 3A fuse in the plug? Safer.
 
Hopefully a typo, but judging by some of your comments here and previously (multiple spurs from a single Wago springs to mind) I’d not be surprised if that was true.
It was amazing how many could not figure that out, which was so simple. You need to look at Wagos.
 
You are an electrician aren't you. We work to the regs.
It would be 'electrically incorrect' as it would be marked as a deviation from the regs in a report.
Show me the reg that says local isolation is mandatory? Whatever local isolation is of course. Where should this non-mandatory local isolation be? in a cupboard? Over a worktop? In an adjacent utility room? Under an appliance? Where?
 
Last edited:
I my point it is not the end of. Only going by regs is not what competent electricians should be doing. Sometimes you have to use the electrical knowledge and training they are given.

Would that be the same knowledge and training that started this thread with the suggestion of 1mm cable and a 3A fuse?
 
No reg says local isolation is needed.
You should work to your electrical training and knowledge, not be like one of these, rear end covering, moronic, reg followers.
Fair enough if you wish to argue a point but posts like this will see the thread closed.
 
No reg says local isolation is needed.
You should work to your electrical training and knowledge, not be like one of these, rear end covering, moronic, reg followers.

Show me the reg that says local isolation is mandatory? Whatever local isolation is of course. Where should this non-mandatory local isolation be? in a cupboard? Over a worktop? In an adjacent utility room? Under an appliance? Where?

We are talking about you saying that 1mm is 'electrically correct' for the circuit. Don't try and change the subject because you are wrong and know it mate. Have a look at the table I mentioned in a previous post for the reg.
 
We are talking about you saying that 1mm is 'electrically correct' for the circuit. Don't try and change the subject because you are wrong and know it mate. Have a look at the table I mentioned in a previous post for the reg.
A sole appliance, on a radial, drawing a third of an amp, on 1.00mm cable on say a 10A mcb is electrically sound and safe. Are you saying it is not?
 
We are talking about you saying that 1mm is 'electrically correct' for the circuit. Don't try and change the subject because you are wrong and know it mate. Have a look at the table I mentioned in a previous post for the reg.
You are supposed to be electrically trained. To think. Now do not look at table. Tell me where it is electrically not sound or safe? I will be waiting a long time.
 
Status
Not open for further replies.

Reply to Fuse too big on fridge in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top