hi everyone

if i had a fault on an outside socket and the fused spur was switched off inside what controls outside socket would it still trip the rcd

hope that makes sense
 
woah opened up a can of worms here then lol

right i have a switched fused spur off the ring wheich feeds a outside socket

now if this fused spur was switched off and i had a fault on outside socket would it trip

are all switched fused spurs double pole if so im guessing you cant as your breaking line and neutral conections and only the cpc will still goto the socket

if single pole it would only break the line so if i had a fault between neutral earth it would still trip even if switched off id of thought


its like when u cut through a cable when breakers off but rcds on it detects an inbalance and trips rcd



does that sound right lol
 
woah opened up a can of worms here then lol

right i have a switched fused spur off the ring wheich feeds a outside socket

now if this fused spur was switched off and i had a fault on outside socket would it trip No



if single pole it would only break the line so if i had a fault between neutral earth it would still trip even if switched off id of thought

does that sound right lol

Not a chance! You need a circuit for current to flow to your outside socket - with line disconnected (switched off) you have no circuit, so no current

its like when u cut through a cable when breakers off but rcds on it detects an inbalance and trips rcd

This, also, would not happen:)
 
Not a chance! You need a circuit for current to flow to your outside socket - with line disconnected (switched off) you have no circuit, so no current



This, also, would not happen:)


Wayne have i read this right ,, u are saying that if you cut through a cable that has the mcd turned off but is still connected at the board,, it wont trip,,

If so you are totally wrong as the RCD will trip ..
 
If you only break the live conductor ie turn it off at the breaker or single pole devise and it's RCD protected then you touch the earth down to the neutral of that circuit the RCD will trip.
 
If, on the RCD side of the board, you have the MCB for a circuit, (say your ring final), open (off) - you could connect the neutral and earth of that circuit together in a choc bloc and it isn't gonna trip the RCD!

You really need to read up on how a circuit operates and how an RCD operates.:)


If you don't believe me, try it:D
 
Last edited by a moderator:
If, on the RCD side of the board, you have the MCB for a circuit, (say your ring final), open (off) - you could connect the neutral and earth of that circuit together in a choc bloc and it isn't gonna trip the RCD!

You really need to read up on how a circuit operates and how an RCD operates.:)


If you don't believe me, try it:D

So your saying to disconnect the neutrals and CPCs of that circuit from their respective bars and put them in block and this won't trip the RCD? when I said to touch the earth down to neutral I meant at the end of that circuit not in the board.
 
Last edited by a moderator:
So your saying to disconnect the neutrals and CPCs of that circuit from their respective bars and put them in block and this won't trip the RCD? when I said to touch the earth down to neutral I meant at the end of that circuit not in the board.

No, I mean connect them together at the end of the circuit - (eg. the Ops outside socket)

The only time it would trip the RCD is if enough current was flowing from other loads(circuits) on the same RCD - and some of this current flowed up the neutral of the fault circuit and down to earth (parallel path).
This would obviously depend on impedances of cables etc.

But if no other circuit was under significant load, then, as I said, it's not possible for a neutral/earth fault on an isolated circuit to trip the RCD.

If you only break the live conductor ie turn it off at the breaker or single pole devise and it's RCD protected then you touch the earth down to the neutral of that circuit the RCD will trip.

If this were true then we would all be in danger whenever we worked on an isolated circuit - because, what do you do - open MCB on circuit, then test L-N, L-E, N-E with your voltage indicator - all clear and off to work you go:)

But, if the neutral is gonna leak enough current to earth to trip the RCD, then we're in trouble:confused:
 
Last edited by a moderator:
Yes you are correct but nine times out of ten every other circuit is on and is leaking a slight current down the neutral, we are talking real world situations not text book scenarios and i wouldn't have disputed what you said if I hadn't interpreted the OP situation as a real world problem.
 
Reading back over everything, I'm beginning to think I might have got hold of the wrong end of the stick with regards what was being asked.:)

I was thinking more in single circuit scenario - where if the MCB is off - that circuit is dead and can't possibly trip an RCD.

it's clearer now that in certain circumstances a neutral/earth fault could cause a problem for the whole installation.

That's the good thing about these discussions - it gets you thinking:D
 

Reply to fused spur and faults in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
844
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
967

Similar threads

  • Question
It can be easy to lose the sequence of things. If the fused spur has a neon indicator and this isn’t coming on then I wonder if -the original...
Replies
6
Views
934
K
  • Question
Ah, I see. The op question is ambiguous, and I took it that he wanted to add a socket for a washing machine from and exiting switch fused spur. A...
Replies
10
Views
892

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top