woah opened up a can of worms here then lol
right i have a switched fused spur off the ring wheich feeds a outside socket
now if this fused spur was switched off and i had a fault on outside socket would it trip No
if single pole it would only break the line so if i had a fault between neutral earth it would still trip even if switched off id of thought
does that sound right lol
its like when u cut through a cable when breakers off but rcds on it detects an inbalance and trips rcd
Not a chance! You need a circuit for current to flow to your outside socket - with line disconnected (switched off) you have no circuit, so no current
This, also, would not happen
If you only break the live conductor ie turn it off at the breaker or single pole devise and it's RCD protected then you touch the earth down to the neutral of that circuit the RCD will trip.
If, on the RCD side of the board, you have the MCB for a circuit, (say your ring final), open (off) - you could connect the neutral and earth of that circuit together in a choc bloc and it isn't gonna trip the RCD!
You really need to read up on how a circuit operates and how an RCD operates.
If you don't believe me, try it
So your saying to disconnect the neutrals and CPCs of that circuit from their respective bars and put them in block and this won't trip the RCD? when I said to touch the earth down to neutral I meant at the end of that circuit not in the board.
If you only break the live conductor ie turn it off at the breaker or single pole devise and it's RCD protected then you touch the earth down to the neutral of that circuit the RCD will trip.