hi everyone
if i had a fault on an outside socket and the fused spur was switched off inside what controls outside socket would it still trip the rcd
hope that makes sense
Reading back over everything, I'm beginning to think I might have got hold of the wrong end of the stick with regards what was being asked.:)
I was thinking more in single circuit scenario - where if the MCB is off - that circuit is dead and can't possibly trip an RCD.
it's clearer now that in certain circumstances a neutral/earth fault could cause a problem for the whole installation.
That's the good thing about these discussions - it gets you thinking:D
exactly what this site is all about
Not a chance! You need a circuit for current to flow to your outside socket - with line disconnected (switched off) you have no circuit, so no current
This, also, would not happen:)
Oh yes it would. Well remember learning this one, switched offthe lighting circuit so I could chop a cable leaving the vet downstairs to carry on submitting his online annual accounts..........
Yep, sorry mate, but a neutral fault will usually trip an RCD, whether the mcb is on or not. In my time, I've cut plenty of T+E's without thinking, causing the main RCD to trip.
More reading needed;)
Reply to fused spur and faults in the Australia area at ElectriciansForums.net
It can be easy to lose the sequence of things. If the fused spur has a neon indicator and this isn’t coming on then I wonder if -the original...
K
Ah, I see. The op question is ambiguous, and I took it that he wanted to add a socket for a washing machine from and exiting switch fused spur. A...