Fused spur wired off cooker switch | on ElectriciansForums

Discuss Fused spur wired off cooker switch in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 28, 2013
Messages
25
Reaction score
2
Location
Truro
Hi everyone was looking for some advice on a job that I looked at last night. The house has a new boiler being installed which needs a supply to it. There is an existing cooker switch wired in 6mm on a 30A fuse going to a single socket which the electric oven is plugged into. There is also a switched fused spur directly adjacent to the cooker switch wired in 2.5mm which used to supply an extractor fan. Is it ok to connect the new boiler to this fused spur or is the cooker required to be on its own separate circuit? There is also no RCD protection on the existing old Wylex board which uses bs1361 fuses. Thanks in advance!
 
can't see a problem here. the FCU is already energised i assume, so you are not making any alterations to the fixed wiring. therefore the lack of RCD is irrelevant. i'd certainly consider upgrading the CU though.
 
Thanks for all the prompt replies I will check the manufacturers instructions later and also advise on upgrading the cu.

If the instructions are from a European/Scandinavian country manufacturer, (and most are these day's) then you can take most of the requirments with a pinch of salt!! Comply with BS7671 and you can't go far wrong....
 
If the instructions are from a European/Scandinavian country manufacturer, (and most are these day's) then you can take most of the requirments with a pinch of salt!! Comply with BS7671 and you can't go far wrong....

Here we go again... 7671 says to follow man. instructions, so regardless of what we think, it's part of the regs. ;)
 
Here we go again... 7671 says to follow man. instructions, so regardless of what we think, it's part of the regs. ;)


As i told you before, you're welcome to blindly follow whatever instructions you want too. Those that have a bit of commonsense, will not blindly follow manufacturers instructions that are directing you away from BS 7671 towards other countries requirements.

BS 7671 is not a statutory British standard, it's advisory and guidance/recommendatory oriented, that contradicts itself time and time again throughout the publication.
 
As i told you before, you're welcome to blindly follow whatever instructions you want too. Those that have a bit of commonsense, will not blindly follow manufacturers instructions that are directing you away from BS 7671 towards other countries requirements.

BS 7671 is not a statutory British standard, it's advisory and guidance/recommendatory oriented, that contradicts itself time and time again throughout the publication.

Please don't tell me that I have no commonsense. Come back and run your own business in this modern England before judging any calls I make!
 
Aye follow manufactures instructions and comply with bs 7671 . We getting wrapped up here in personal opinions when it clearly states follow manufactures instructions and If there's a problem and goes to court and you can prove you followed bs7671 , you a free man. There won't be much difference.. Between two guides of info .

All manufactures data should be followed but installed within bs7671. Come on it ain't that hard..
 

Reply to Fused spur wired off cooker switch in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It can be easy to lose the sequence of things. If the fused spur has a neon indicator and this isn’t coming on then I wonder if -the original...
Replies
6
Views
975
You only need to switch the lines and the contactor is rated per pole so for example a 16A four pole contactor would be fine.
Replies
1
Views
317

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top