Hi Guys.
Just done a rewire which includes a 32 Amp 6mm cooker supply to a cooker outlet point via the usual isolator + socket.

This is only being used for an oven which turns out to be 2.7 Kw, with an HR 1.5mm flex requiring a 13 Amp fuse.

Would it be acceptable to change the outlet point to an FCU (which will be hidden behind the oven)? Guess that's no worse than having a hidden plug and socket! Not quite sure whether 6mm cores will fit in a FCU, but I'm always willing to try!
Cheers.
Pete
 
Well you see it's like this, the problem is............errrm...............the problem is..............hmmmm..........no i'm stumped, over to you piratepete!

MCB is 32 Amp. Oven requires 13 Amp. Considered changing MCB to 16 Amp but this also supplies socket on isolator which could have a 3 kw kettle plugged into it. Simple,eh? 13 Amp is manufacturer's requirement (fan oven)
 
Last edited by a moderator:
6mm to a surface 13a skt behind the oven to fuse it down.
Had to do similar many times and sometimes a twin socket for the oven and gas hob ignitor.
The oven manufacturers are miserable with the flex length so maybe change it?
Boydy
 
Jesus, .....either change the MCB rating to 16A/20A if you're that worried about it, or just leave it as it is!! The oven is classed as a ''fixed load'', so cannot overload. the MCB of any of the above ratings will protect against short circuit faults!!


What do you think happens in the rest of Europe, where the same oven is sold?? There are no fused socket outlets or FCU's.

Oh and BS 1362 fuses are there to protect cables/cords/leads, not the appliances to which they are attached!!!
 
The last 6 ovens I have wired up did not come with any flex at all.

Then they are even more miserable nowadays.
PP is talking about a single cavity oven with selector switch which means either the oven or grill can be used, therefor the load is 2.7kw.
A traditional double or one and half oven however doesnt usually come prewired.

Boydy
 
MCB is 32 Amp. Oven requires 13 Amp. Considered changing MCB to 16 Amp but this also supplies socket on isolator which could have a 3 kw kettle plugged into it. Simple,eh? 13 Amp is manufacturer's requirement (fan oven)

MCB is 32A cable is 6mm, MCB is correctly sized for cable (the thing it is there to protect) no overload protection is required as per the regulations (loads which by their nature cannot suffer overload) just check that the 1.5mm flex to the oven is suitably covered for fault protection.

Also suggest you check the diversity tables for how much you should be allowing for a socket outlet in a cooker switch.
 
THE PROBLEM IS THAT OLS CHESTNUT " MANUFACTURERS INSTRUCTIONS". IF YOU DON'T FUSE IT DOWN TO 13a, THEY CAN DISCLAIM RESPONSIBILITY IF AND WHEN IT GOES WRONG.
 

Reply to Fusing down the oven. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Replies
9
Views
2K
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top