I'm in the middle of putting some lighting and socket outlets in my garage, nothing fancy just a few of each as you'd expect. I've run it in SWA ,which will be buried eventually, from the existing CU in the house on it's own circuit. Earthing arrangement is TT which reads 14.67 ohms, not bad I thought been in for 20+ years.
There's a cold water feed coming from the house underground and pops back up in the garage, now this is bonded as you'd expect in the house back to the MET which reads 0.54 ohms when testing against the new garage CU earth bar. So this got me thinking... it isn't extraneous as testing shows it's already connected, nor is this a separate dwelling so in effect is within the same installation.
My gut feeling is to supplementary bond it regardless due to risk of introducing a difference in potential should there be an issue with the main bond in the house, but as far as the regs are concerned???
Thoughts?
There's a cold water feed coming from the house underground and pops back up in the garage, now this is bonded as you'd expect in the house back to the MET which reads 0.54 ohms when testing against the new garage CU earth bar. So this got me thinking... it isn't extraneous as testing shows it's already connected, nor is this a separate dwelling so in effect is within the same installation.