Spearmint

I'm in the middle of putting some lighting and socket outlets in my garage, nothing fancy just a few of each as you'd expect. I've run it in SWA ,which will be buried eventually, from the existing CU in the house on it's own circuit. Earthing arrangement is TT which reads 14.67 ohms, not bad I thought been in for 20+ years.

There's a cold water feed coming from the house underground and pops back up in the garage, now this is bonded as you'd expect in the house back to the MET which reads 0.54 ohms when testing against the new garage CU earth bar. So this got me thinking... it isn't extraneous as testing shows it's already connected, nor is this a separate dwelling so in effect is within the same installation.

My gut feeling is to supplementary bond it regardless due to risk of introducing a difference in potential should there be an issue with the main bond in the house, but as far as the regs are concerned???

Thoughts?
 
I'm in the middle of putting some lighting and socket outlets in my garage, nothing fancy just a few of each as you'd expect. I've run it in SWA ,which will be buried eventually, from the existing CU in the house on it's own circuit. Earthing arrangement is TT which reads 14.67 ohms, not bad I thought been in for 20+ years.

There's a cold water feed coming from the house underground and pops back up in the garage, now this is bonded as you'd expect in the house back to the MET which reads 0.54 ohms when testing against the new garage CU earth bar. So this got me thinking... it isn't extraneous as testing shows it's already connected, nor is this a separate dwelling so in effect is within the same installation.

My gut feeling is to supplementary bond it regardless due to risk of introducing a difference in potential should there be an issue with the main bond in the house, but as far as the regs are concerned???

Thoughts?

Is the house DB TT or have you just done this at the garage DB?
 
The test for an extraneous part must be carried out with the earthing conductor disconnected from the MET of disconnect link open.

The test you have carried out with all main bonds connected is what you would do to establish whether supplementary bonding is required or not
 
The test for an extraneous part must be carried out with the earthing conductor disconnected from the MET of disconnect link open.

The test you have carried out with all main bonds connected is what you would do to establish whether supplementary bonding is required or not
Disconnected? Surely all metallic pipework would appear extraneous if you tested against the main earthing conductor disconnected? I have quickly tested against the garage CU (only because I was in there) which returned 0M ohms... will be going back with a wander lead to test this weekend hopefully!
Do what dave said to establish if it's extraneous or not then if it requires bonding the CSA of the SWA you have installed is to small. So you will have to replace the SWA or run in a separate bond.
Thought of that already, was going to get a length of G/Y when I stopped and questioned myself whether or not this actually required bonding.
 
There's a cold water feed coming from the house underground and pops back up in the garage, now this is bonded as you'd expect in the house back to the MET

Why would you need to test this water pipe?/ If it's metal and has been directly buried underground to the garage it's gonna be extraneous without a shadow of a doubt. It doesn't matter a jot whether the incoming metal water pipe has been main bonded at the house, it will still need bonding at the garage to the garages EMT...
 
Why would you need to test this water pipe?/ If it's metal and has been directly buried underground to the garage it's gonna be extraneous without a shadow of a doubt. It doesn't matter a jot whether the incoming metal water pipe has been main bonded at the house, it will still need bonding at the garage to the garages EMT...

Would it though ?, if the garage is integral to the house (part of the same building).

I would probably add the extra bond if it was easy enough to do, but would it actually require it ? I would personally say not in this case.
 
Would it though ?, if the garage is integral to the house (part of the same building).

I would probably add the extra bond if it was easy enough to do, but would it actually require it ? I would personally say not in this case.


If it's an integral garage it would be one and the same equipotential zone, and the power and lighting circuits would i imagine be supplied from the house CU.
 
If it's an integral garage it would be one and the same equipotential zone, and the power and lighting circuits would i imagine be supplied from the house CU.


That is how I would treat it, the OP said it is integral, this is really no different to having a separate additional CU in any other room in the house.

I would agree if the building was separate :)
 
I'm in the middle of putting some lighting and socket outlets in my garage, nothing fancy just a few of each as you'd expect. I've run it in SWA ,which will be buried eventually, from the existing CU in the house on it's own circuit. Earthing arrangement is TT which reads 14.67 ohms, not bad I thought been in for 20+ years.

There's a cold water feed coming from the house underground and pops back up in the garage, now this is bonded as you'd expect in the house back to the MET which reads 0.54 ohms when testing against the new garage CU earth bar. So this got me thinking... it isn't extraneous as testing shows it's already connected, nor is this a separate dwelling so in effect is within the same installation.

My gut feeling is to supplementary bond it regardless due to risk of introducing a difference in potential should there be an issue with the main bond in the house, but as far as the regs are concerned???

Thoughts?

Here in bold, now as to whether it is the type of garage with a doorway into the house is another matter ;)
 

Reply to Garage Metalwork in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top