cliffed

-
Arms
Joined
Dec 20, 2009
Messages
2,186
Reaction score
698
Location
Worcester
Finished a Eicr,just your thoughts on this,the remote garage is supplied from the ring main of the house,other building are radials of this.
The supply enters from underground,& are pvc t&e,goes straight into a 2g power point,then to other points.
There is no main bonding required,thinking this needs isolation when entering the building,& other supplies protected accordingly.
Would you fit a small DB on the main in,or a complete no no,cause it’s a ring main.
 
If I've understood correctly the garage has an underground supply from the house using t&e. If so, likely this can not comply without replacing the run with SWA.
Re the C2 of the report - I don't understand the potential safety issue of not having a means of isolation separate from the outlet? Unless it's for emergency switching perhaps (Table 53.4).
 
Yes, the OP says the garage circuit is part of the house ring. Two T&E cables going underground from the house to the garage.
Looks to me like the report is rubbish and false. Why does the garage need isolation?
 
Yes, the OP says the garage circuit is part of the house ring. Two T&E cables going underground from the house to the garage.
Looks to me like the report is rubbish and false. Why does the garage need isolation?
Well that’s what I asked in my first post,you don’t think it’s needs isolation,most supplies do,but thanks for your input.
 
Well that’s what I asked in my first post,you don’t think it’s needs isolation,most supplies do,but thanks for your input.
The problem here is the C2 from the Report makes no sense, isolation at garage. The person who did this I imagine was trying to say multiple outlets in the garage are spurred from the ring final circuit with no provision for suitable circuit protection. I would go back to the Report author for them to clarify it.
 
Yes, the OP says the garage circuit is part of the house ring. Two T&E cables going underground from the house to the garage.
Looks to me like the report is rubbish and false. Why does the garage need isolation?
If there are two cable entering the Garage, then the possibility that the supply to the garage is/must be part of the RFC and not a spur, it need clarification, before decisions can be made in my opinion. Do the 2 cables form part of the RFC or are they something else?
 

Reply to Garage & other external buildings in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
501
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
974
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
497
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top