For a change its nice to have a clean slate to work to. Client wants their garage rewired (and boy does it need it!) so they can have the following:
Washing Machine, Tumble Dryer, American Fridge/Freezer, Outside socket, outside lights, workshop tools all 13A type such as circular saw etc.
Garage already has a 6mm cable connected back to the house consumer board via a 32A MCB and is RCD protected.
The existing cabling is a real rats nest and just isn't suitable for purpose, so its all being ripped out along with the old Wylex rewireable fuse board which just hasn't been wire correctly - I suspect multiple DIY'ers over the years have just added things into it.
Anyway I digress. My thoughts were this.
New consumer unit with a 63A main switch (7 available ways), existing 6mm cable terminated into it.
All cables can be clipped direct as it's in a garage with an open truss roof so loads of room to run cables neatly.
All the "kitchen" type appliances on a 4mm radial to a 32A MCB.
Workshop appliance(s) on a 2.5mm radial to a 20A MCB. This should be adequate to deal with any inrush current.
Outside socket on it's own 2.5mm radial to a 20A MCB.
Indoor lights on a 1.5mm 6A MCB
Outdoor lights on a 1.5mm 6A MCB
Giving the client an extra 2 ways if necessary for expansion.
Yes I suppose I could put the kitchen appliances on a ring, but its extra cabling and given I can do clipped direct I can do a 4mm radial on a 32A breaker (4mm is 37A clipped direct).
Could I get away with a 16A MCB for the tools ? Well, perhaps given they aren't industrial grade tools, just the ones you would get from a DIY store, but I want to allow for any inrush current, a 10A would probably trip.
Yes it would be better to tap off the incoming tails via a Henley block, but there is no isolator switch which means pulling the 100A fuse if I wanted to do it - just seems too much for this particular job.
If I've worked this all out correctly, the 6mm cable back to the 32A MCB should be more than adequate unless everything was running at the same time at full load all the time, which is highly unlikely. I suppose I could up it to a 40A MCB, but I don't think its necessary.
Just wondered what other peoples thought were on this.
Washing Machine, Tumble Dryer, American Fridge/Freezer, Outside socket, outside lights, workshop tools all 13A type such as circular saw etc.
Garage already has a 6mm cable connected back to the house consumer board via a 32A MCB and is RCD protected.
The existing cabling is a real rats nest and just isn't suitable for purpose, so its all being ripped out along with the old Wylex rewireable fuse board which just hasn't been wire correctly - I suspect multiple DIY'ers over the years have just added things into it.
Anyway I digress. My thoughts were this.
New consumer unit with a 63A main switch (7 available ways), existing 6mm cable terminated into it.
All cables can be clipped direct as it's in a garage with an open truss roof so loads of room to run cables neatly.
All the "kitchen" type appliances on a 4mm radial to a 32A MCB.
Workshop appliance(s) on a 2.5mm radial to a 20A MCB. This should be adequate to deal with any inrush current.
Outside socket on it's own 2.5mm radial to a 20A MCB.
Indoor lights on a 1.5mm 6A MCB
Outdoor lights on a 1.5mm 6A MCB
Giving the client an extra 2 ways if necessary for expansion.
Yes I suppose I could put the kitchen appliances on a ring, but its extra cabling and given I can do clipped direct I can do a 4mm radial on a 32A breaker (4mm is 37A clipped direct).
Could I get away with a 16A MCB for the tools ? Well, perhaps given they aren't industrial grade tools, just the ones you would get from a DIY store, but I want to allow for any inrush current, a 10A would probably trip.
Yes it would be better to tap off the incoming tails via a Henley block, but there is no isolator switch which means pulling the 100A fuse if I wanted to do it - just seems too much for this particular job.
If I've worked this all out correctly, the 6mm cable back to the 32A MCB should be more than adequate unless everything was running at the same time at full load all the time, which is highly unlikely. I suppose I could up it to a 40A MCB, but I don't think its necessary.
Just wondered what other peoples thought were on this.